I am just looking for a second opinion on a condition report I have had done on a rental property I have. I had a report done as to check the condition of the electrics and have been told that on the lighting and sockets there is no continuity of conductors yet the certificate has been completed including boxes for R1+R2, IR and ZR. I have googled it and if there is no continuity it seems to me that there would be no readings. I’m not an electrical expert but it has confused me and so I was looking for some advise, perhaps a retest? I have a few rental properties so there will be more work moving forward, thank you ?
 
It is possible that there is continuity to some sockets/lights (where R1+R2 can be taken) and not to others, so the C2 code might only be for one fixing or room (The observations should make this clear ideally).

With the sockets, if they are on a Ring Final Circuit (32A breaker usually), then the lack of continuity may suggest that the loop is not complete for the cpc (earth), This would give a reading for R1+R2 & Zs at each socket, but would still need to be resolved - however, it is sometimes as simple as a loose connection in a socket or junction box.

If yoiu want to post a copy with identification removed, we can look at it and give you a better idea, but it may be worth seeking clarification. The remedial works for a missing earth could be anywhere from simple to a complete rewire so it's hard to be more definitive without more information.
 

Reply to Electrical testing in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
669
The instructions tell you to test the insulation and you already know from the result of the previous test that the L and N are not insulated from...
Replies
4
Views
532
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top