Hello,
I'm in TT world. I got ELR tripping here. ELR having protection the several small circuit which have RCCB. When i test using RCCB tester at downward circuit which has RCCB, the ELR will tripped. What is the problem here? Using discrimination it should RCCB that should trip.
 
Yup, the circuit coming from main switchboard which has ELR at the sensitivity of 0.5A at time delay 50ms. At the bulding sub-switchboard, there is ELR at the sensitivity of 0.3A at time delay 50ms. From the sub-switchboard there are several circuit going out which having protection of RCCB of sensitivity 0.3A and 0.1A at instanteneous time. The problem here when I having RCCB test at downstream circuit at each circuit having the RCCB protection, the ELR at sub-switchboard tripped. Shouldn't be happen as the current & time discrimination are already there.

The ELR also tripped even at no trip test of RCCB test.

ELR also tripped even at no trip test of RCCB.

Already replace the ELR,tripping is still there. But, when i test the terminal at zct using test pen, there is voltage there. In my knowledge, there shouldn't be a voltage there as in normal circuit there should be a balance current. So should not have a voltage.It is possible the tripping is due to the faulty zct???
 
Last edited by a moderator:

Reply to ELR Tripping in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
267
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
754

Similar threads

My guess is an earth to N fault in the damaged light fitting. This will become a problem when other devices draw large currents.
Replies
2
Views
338
  • Question
Thank you for taking the time to help explain this - much appreciated
Replies
7
Views
853

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top