Emergency call out for burning cutout | on ElectriciansForums

Discuss Emergency call out for burning cutout in the Australia area at ElectriciansForums.net

Joined
Feb 7, 2009
Messages
360
Reaction score
16
Location
.
I have just been called out when client noticed smoke comming from 2g socket. Thinking this would be more or less straight forward to identify fault and rectify, I advised client to immediately turn off consumer unit and rushed to job in case of fire hazzard. On site, even with consumer unit off, smoke was still pooring from the socket.
Tested socket was dead and removed it to find the smoke was comming up the conduit from the basement where the main cutout was directly below. Once in the basement I found the main incomming cable was to two cutout fuses. One had tails 16mm to Henley block and supplied two upstairs flats each with own 16mm tails and consumer units. The other also had 16mm tails to a henley block which then supplied two downstairs properties each with its own consumer unit.

On sight of cutout both line tails out of each cutout fuse were glowing red with orange sparks falling from them and sheathing burning and melting.
I immediately did my best to isolate all four consumer units so no current was being drawn and called Fire service and YEDL. Smoke was very soon too bad to be able to see. Evacuted building and waited for fire service.

After all sorted and several hours later with power off to whole street, the cutout was replaced with new and new 16mm tails.
YEDL chap said cause probably main supply cable needs upgrading as too big a demand in building for existing. Is this likely as they have just put things as they were but just new parts and tails. So could same thing just happen again. ???
 
They live by there own rules, if it burns out again they will upgrade it if its ok it was a bad joint in cutout.... its how they work ...Yes i know if we operated like that we'd have legal costs hitting the roof.
 
probably,sounds as though service fuse is bigger than the maximum size for 16 mm tails,so unless he has put smaller rated fuse in eg 60 amp instead of 100 then yes it could quite well happen again.
 
I don't feel I can leave things as they are but now new cutouts in and sealed i cannot identify the fuse size.
I will contact YEDL tommorrow for the info am i likely to get it.
 
If domestic I'd suspect dodgy connection rather than overloading. Never seen cables glowing red before tbh, felt them really hot but never glowing.

Could get the home owner to power everything up and get a clamp meter onto the tails to see what they are pulling.
 
[ElectriciansForums.net] Emergency call out for burning cutout

[ElectriciansForums.net] Emergency call out for burning cutout
not sure,havnt read it but info here
 

Reply to Emergency call out for burning cutout in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
791
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
817

Similar threads

This was posted this week, on topic ....... https://niceic.com/newsletter/omission-of-overload-protection/?dm_i=7G1W,7GCE,K4L2A,WHET,1
Replies
8
Views
702
  • Question
Normally you'd install either a fuse-switch or a switchfuse at the incoming supply position rather than a DB, this gives you some hope of...
Replies
10
Views
1K
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top