Many of our sites do not have emergency lighting installed, which I find strange as they are busy high street shops and can contain 10-20 customers at any one time.
Is there any regs that state all buildings (new or existing) serving customers must have emergency lighting?
Thanks
Pete
BS5266-1:2005 5.2
Under the Management of Health and Safety At Work Regulations 1999 [7], every employer is required to carry out a risk assessment to identify the risk to people who enter the employer’s premises; the employer is required to take measures on the basis of the risk assessment to safeguard building occupants. These measures need to include the provisions of safe means of escape, including, where necessary, emergency lighting, taking into account the needs of people with disabilities, In particular people with visual impairment.
A shop capable of holding 20-30 customers who will be unfamiluir with the layout, Location of life saving equipment and emergency escape routes, I would say needs emergecy lighting.
Not just to illuminated the escape routes, but also firefighting equipment, call points etc etc
If the lights go out, and there is a fire, no one apart from shop employees, who maybe dead, will know where the fire extinguisher are.
You could also look at it this way. If the lights go out and its pitch black, will there be a need to secure drugs before leaving the building?