Hi, first post, had a quick search, couldn't find my problem so here goes.....went to check on some failed em. lighting which had come up on a monthly test. Downlighters with 2x26w flourescent pl lamps in, 1x2 pin 1x4 pin connections...anyway someone had relamped both sides with 2 pin lamps, but they were working as normal(but not in emergency mode). When I changed the obviously wrong 2 pin for correct 4 pin lamps, they would not work as normal(but would work in emergency mode). inside the fitting there is a 26w wire wound ballast and an em.module(+battery etc). Anybody got any thoughts. Im thinking wrong lamps have damaged the em.module ?
 
somebody has removed a wire link from the emergency Ballast? if the lamps were changed to the wrong type they may have been forced to do this, the 4 pin lamp would have been the emergency one that got maintained, then swapped to two 2 pin lamps as probably all they had....check the connections then check the batteries to see if they are holding a charge with a multimeter, if not charged, redo the link wires, power on for a day then see if taking a charge,if not then new battery packs are about ÂŁ10....will be in wholesalers shop in town...
 

Reply to Emergency lighting faults in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
293
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
801
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
833

Similar threads

Fitted a lot of this sort of light recently, with all tests reporting back through central Dali controller(s).
2
Replies
15
Views
942
nicebutdim
N
The challenge that you have with this is that you've no confirmed start point. Because you have a lack of an EICR you don't actually know what...
Replies
7
Views
585

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top