Hi, does anyone know what you would put in the boxes on page 2 of the EL PIR the section I am referring to is part I - categories of operation.
I have seen a completed cert and these boxes seem to have X's and O's in the boxes what do these mean???
7.10 Categories of operation of emergency lighting systems
Categories of operation are specified in BS EN 50172:2004/BS 5266-8:2004, 5.6.
In this standard, emergency lighting systems are classified according to the following parameters, as given for luminaires in BS EN 60598-2-22:1999, Annex B:
a) Type:
X self-contained;
Y central supply;
b) Mode of operation:
0 non-maintained;
1 maintained;
2 combined non-maintained;
3 combined maintained;
4 compound non-maintained;
5 compound maintained;
6 satellite;
c) Facilities:
A including test device;
B including remote rest mode;
C including inhibiting mode;
D high risk task area luminaire;
d) Duration of emergency mode (in minutes) for a self-contained system:
10 to indicate 10 min duration;
60.............1 h duration;
120............2 h duration;
180............3 h duration.
Previously, emergency lighting systems were categorized by the prefix “M” for maintained and “NM” for non-maintained systems, followed by an “/” and the number of hours duration claimed for the installation, e.g. for self-contained systems:
M/1 was a maintained 1 h duration system; this is now [X][1][****][60]
NM/3 was a non-maintained 3 h duration system; this is now [X][0][****][180]
NOTE **** in the third box stands for the facilities [see item c)], details of which are added, as applicable, at the time of installation.