B

BathSparks

I was asked recently to add a couple of sockets into a ring in a local village hall. When I turned off the small fuse board (Fitted with plug-in MCBs). The emergency lights came on.

I was still getting current running through the neutral at a socket on the ring circuit?. The main incoming supply is TT protected by an RCD. When this is turned off, (the whole installation made dead) the ring is dead. Not having much experience of emergency lighting systems I am wondering what is going on here. Will be going back to investigate further. Any ideas as to what is going on here?
 
Hi mate,

No offence intended and I'm sure you mean well by helping the village hall out but, please leave the job to an electrician.

Of course, I am an electrician and I fully expect the emergency lights to come on.

However, the only experience I have had with emergency lights involved self contained units with batteries that energise a lamp when the mains goes. These usually have isolation transformers in them to isolate them from the mains supply.
 
How did you establish that there was current running through the neutral?
First confirmed CU was off
After receiving a small shock, tested with Metrel MI 3112 multifunction tester at socket.
The only experience I have had with emergency lights involved self contained units with batteries that energise a lamp when the mains goes. These usually have isolation transformers in them to isolate them from the mains supply.
 
First confirmed CU was off
After receiving a small shock, tested with Metrel MI 3112 multifunction tester at socket.
The only experience I have had with emergency lights involved self contained units with batteries that energise a lamp when the mains goes. These usually have isolation transformers in them to isolate them from the mains supply.

Ok, doesn't answer how you confirmed current was flowing though.

The shock implies that there was voltage present, where did the current flow come from?

And what has this got to do with emergency lights? It's a socket cct isn't it!
 
Ok, doesn't answer how you confirmed current was flowing though.

The shock implies that there was voltage present, where did the current flow come from?

And what has this got to do with emergency lights? It's a socket cct isn't it!
Tested between Live and neutral, Live and Earth, Neutral and Earth.
That is the reason I am asking these questions. There should be no current flowing if the circuit is turned off. With the CU off, there should not be any current at the sockets.
By turning of the Main RCD, there is no current at the sockets as you would expect. The emergency light are lit, as you would expect. Turning the local board off, however, still leaves current flowing between N and E. at a socket fed from the same board.
 
What reading did you get when doing the above tests
LN = 0
LE = 0
NE =120v
On the circuit I was to add sockets the following readings were added to the MEIWC
IR
LN = 200MΩ
LE = 200MΩ
NE = 200MΩ
Loop imp = 0.37Ω
The Main RCD
Rated current 30 mA
time = 18 ms
Probably too much info here as most of this seems normal enough.
If there is a central inverter, then could be this.
A neon tester at the local board also lit up when on the Neutral busbar.
even with the main switch for this board OFF
Seems to be some kind of 'backfeeding' going on.
 
I was asked recently to add a couple of sockets into a ring in a local village hall. When I turned off the small fuse board (Fitted with plug-in MCBs). The emergency lights came on.

I was still getting current running through the neutral at a socket on the ring circuit?. The main incoming supply is TT protected by an RCD. When this is turned off, (the whole installation made dead) the ring is dead. Not having much experience of emergency lighting systems I am wondering what is going on here. Will be going back to investigate further. Any ideas as to what is going on here?

Not read all but like will of been said, emergency lights are exactly that....when there's an emergency and the lights go out..they kick in running off a battery pack
More investigation is needed me thinks
 
You confirmed consumer unit was off.......... then got a shock pmsl
Correct. The main switch on the sub-board (2 6A, 1 32A and 1 16A) was turned OFF. All the light went off, the emergency light came on (as expected). The sockets were presumed dead. I initially tested this with one of three light testers (again limited in fault finding but ok for this) after unscrewing the front plate, I got the shock and proceeded to further testing.
 

Reply to Emergency lighting problem in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
808
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

Fitted a lot of this sort of light recently, with all tests reporting back through central Dali controller(s).
2
Replies
15
Views
947
nicebutdim
N
  • Question
Or a combined fitting in each row.
Replies
19
Views
2K
nicebutdim