Emergency Lighting Query | on ElectriciansForums

Discuss Emergency Lighting Query in the Australia area at ElectriciansForums.net

W

wallyanker

Hello

Our warehouse manager informed me today that during a 2 minute power cut, the emergency lighting came on and then went off again when the power was restored. I couldnt see the problem until he explained that the big bay lights used to illuminate the picking isles did not come back on for approx 10 mins (400w-600w sodiums I believe). So his staff were stood in the dark waiting for the lights to come back on. :dizzy2:

Can you install any form of time lag switch to the emergency lighting so that when the power is restored, they still continue to work for 10 mins or so?? Picture below is the type of emergency lighting installed in the warehouse.

Thanks
[ElectriciansForums.net] Emergency Lighting Query
 
Only immediate thing I can think of that's going to be fairly simple will be to alter the supply circuit to the emergencies so that they are fed via a contactor, that way when the site comes back on they'll need a manual reset to restore the power supply to turn them off.
 
Another option might be to effectively create the same effect as above, but by using a switched live output from the battery side on one of the units to trigger a shunt trip that feeds the circuit to knock the MCB out.
 
explain to the nice gentleman, that emergency lighting is designed to facilitate an escape only, not to allow his staff to carry on working. To make his staff work in unsafe conditions caused by low lighting levels would be contrary to the HSAW act.
Tell him that you would be happy to change the fittinmgs to induction fittings, that will instantly re-strike, and will save him a fortune on maintenance and energy costs.
 
Last edited:
explain to the nice gentleman, that emergency lighting is designed to facilitate an escape only, to to allow his staff to carry on working. To make his staff work in unsafe conditions caused by low lighting levels would be contrary to the HSAW act.
Tell him that you would be happy to change the fittinmgs to induction fittings, that will instantly re-strike, and will save him a fortune on maintenance and energy costs.

Whilst this is technically reasonably accurate, in the real world we're professionally engaged to solve problems and find solutions, not just be pains in the backside because we think having sat some exams entitles us to ride rough-shod over some non-existant moral high ground. And this profession wonders why it has such a low public opinion?????!!
 
im being serious. It would be irresponsible of us to try and facilitate a means of allowing people to work, in low lighting conditions. Especailly in an environment, where the order pickers are required to read small writing.
were not being pains in the backside, by pointing out the obvious.

My second suggestion in the my post is a reasonable, economically sensible decision.
 
Hence my saying that I'm not technically in disagreement with you.

There is actually a counter argument though that says a short duration power down of just a few seconds would actually lead to a far more dangerous situation as it would leave a large building in darkness for a period, full of staff in mid activity, when the emergencies have gone off but the main lights not back on. Hmmm.....anyone up for some blind man forklift driving?

Faced with two options - 1) find a ÂŁÂŁ-ÂŁÂŁÂŁ solution or 2) have a hissy fit and insist upon a ÂŁÂŁÂŁÂŁÂŁ solution, I know which of the two any business in this country is going to choose at the moment. The first saving they'd make would be to get rid of the OP!!
 
Last edited:
Does seem like a risk assessment wasn't carried out when the lighting & em lighting was originally installed.

IMO this situation needs addressing ASAP as the employer could be leaving himself open to all manner of issues should any member of the workforce injure themselves whilst working during this period of time whilst waiting for the lights to re strike.
 
Can you install any form of time lag switch to the emergency lighting so that when the power is restored, they still continue to work for 10 mins or so??

You can get configurable timers (DIN rail mounted) which can be set from seconds to hours or even days.

This would need to be set to give the required delay at 'power on'

These can be set in a variety of ways, I think you would need to delay the permanent live feed to each Em. Lamp, and so may need one for each fitting, or alternatively a single one if all of your permanent lives (for the EM lamps) are commoned.

Here is such a relay as an example.
 

Attachments

  • CRM-91H,93H,9S.pdf
    408.1 KB · Views: 20

Reply to Emergency Lighting Query in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
301
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
814
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
873

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top