We have been asked for a second opinion by a company we do a fair bit of work for.
They have had an emergency lighting full duration test conducted and we have now followed up with a second test.
The test related to a large ware house with self contained spot floods fitted around the perimeter and centre RSJ's
Only 2 of the units failed in under 120 minutes, the rest lasted up to 120 to 140 minutes.
The other company suggests replacement of all 22 units because non lasted 180 minutes ??
My issue with this is that the entire installation has generator back up, should mains failure occur.
Also the emergency lighting is to be used for evacuation of the building ??
I explained that my view is that a 1 hour duration should be compliant if supported by a risk assessment.
The generator has a 6 monthly service schedule with load tests and the check its running for an hour on a weekly basis.
Log books for the e/m's are kept on site and all in order.
I said it may be wise for there local fire officer to have some input but that I honestly felt replacement of the fittings wasn't needed.
Some people are just scamming for work, and the price for replacement was astronomical which is why the facilities manager wanted our opinion.
I know there are some bright sparks on this forum and wondered if you guys would feel the same way I did.
Cheers lads :winkiss:
They have had an emergency lighting full duration test conducted and we have now followed up with a second test.
The test related to a large ware house with self contained spot floods fitted around the perimeter and centre RSJ's
Only 2 of the units failed in under 120 minutes, the rest lasted up to 120 to 140 minutes.
The other company suggests replacement of all 22 units because non lasted 180 minutes ??
My issue with this is that the entire installation has generator back up, should mains failure occur.
Also the emergency lighting is to be used for evacuation of the building ??
I explained that my view is that a 1 hour duration should be compliant if supported by a risk assessment.
The generator has a 6 monthly service schedule with load tests and the check its running for an hour on a weekly basis.
Log books for the e/m's are kept on site and all in order.
I said it may be wise for there local fire officer to have some input but that I honestly felt replacement of the fittings wasn't needed.
Some people are just scamming for work, and the price for replacement was astronomical which is why the facilities manager wanted our opinion.
I know there are some bright sparks on this forum and wondered if you guys would feel the same way I did.