A

alland1979

Hi Guys,

Just posting to see if any of you guys know if there is a regulation or any form of guidance for the replacement of batteries in emergency light fittings? Is it just change them out when they dont work or is it better to change them over after a set period say 3 or 5 years? Ive tried contacting YUASA and CHLORIDE but have not had any replies back from them so far. The batteries are ni-cd types and range from 2 cell to 4 cell. Thanks in advance:D
 
Cheers for the quick response mate, the batteries are marked up MARCH 2008 but i think thats the factory fitting date rather than the install date. Im looking for a regulation or recommendation so i can go back to my manager and maybe order all the replacement batteries and fit them rather than order them in dribs and drabs and the job will just drag on.
 
The efficiency of the batteries deteriates over time you will probably find the batteries will not last the full test period or the illumination level will be below spec at the end of the test

Nicads will normally last about 3 years and sealed lead acids about 5 years

If you want a gadget for testing then you could try this

Luminaire Battery Tester - test in minutes
 
Cheers for the quick response mate, the batteries are marked up MARCH 2008 but i think thats the factory fitting date rather than the install date. Im looking for a regulation or recommendation so i can go back to my manager and maybe order all the replacement batteries and fit them rather than order them in dribs and drabs and the job will just drag on.

Three years from March 2008 then.( us not reg's )

B.S. 5266, but I dont think you will find anything regarding batt changes other than correct chargiing after 3 hour soak test
 

Reply to Emergency lighting in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
321
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
848
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
971

Similar threads

  • Question
Or a combined fitting in each row.
Replies
19
Views
2K
nicebutdim
N
I don't think I'd use it mate even the one line heading then one long paragraph screams ai. And untrustworthy. I don't think much has been edited...
    • Optimistic
Replies
3
Views
938

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top