Emergency Lighting

T

tuckerkop81

Guys/Gals

I have been given the task at work to ' Sort out ' the emergency lighting. I am new to the job and have little experience as an electrician, but need to do a good job on this one ( first impressions go far! )

I have 2 buildings to get through, 18 floors on each.
Some floors have all lights on, including luminated emergency signs, some floors dont have any luminated signs on. Is there a regulation stating that all emergency lights should be on at all times? One of the floors i had a quick check over didnt have any LED lights to show where the emergency lights are, is this a regulation that needs to be looked at?

Thanks for any other advice that could be of any help!
 
Thanks Lenny

On another note, i was employed some 6 weeks ago, on the job spec i 'only needed' levels 1 and 2 2330 to land the job, which i have. ( taking exams for level 3 now ) In your opinion do you think they are asking a bit too much of me sorting this type of work out? I dont want to start saying im not doing this im not mdoing that as i really enjoy the job, i just dont want to put myself or anyone else for that matter in harms way!
 
I believe that all emergency exits signs should be illuminated at all times.

The best way would be to perform an emergency lighting test and ensure that all lamps and batteries are functioning correctly.

Have the company give the go ahead to change fittings if needs be?

Sent from my HTC Desire using Tapatalk
 
The company i work for has only recently won the contract, and as far as anyones aware there hasnt been a system in place to check these lights. I cant find any wiring diagrames that may help me, some lights work when i push the test button, some lights dont. Some lights are constantly off, some are constantly on, so i beleive from first thought that some floors have been wired differently to others. If any fittings/batteries need changing yes ill have to give an accurate account and theyll order them in for me. I just feel this is going to be one hell of a job trying to find out which lights should be constantly on or off and if its the batteries that are gone or what.

What the final outcome will be is that every month i will perform an emergeny lighting test, turning off all lights for 3 hours to make sure the batteries hold up, i dont want to start that just yet as a hell of a lot of batteries are no doublt gone so will take me longer than the 3 hrs given to replace.
 
Tucker, my company also does a fair amount of e/l testing, though the biggest properties we have are 10 floors, I don't envy you. Definately have a systematic method of working. First work out which are emergency lights, and which should be, all e/l lights should have charge lights illuminated when not being tested. I don't think the e/l's have to be illuminated all the time, it is dependant on whether the other lights are sufficient to provide illumiantion, the only ones that need to be permanently on are the exit signs (I think). Take a look at Lenny's info, it's a good start and has helped me in the past. I also believe a full duration test of 3 hrs is only required once a year, other tests can be 1/3 duration (ie: 1 hr for a 3 hr rated light).
 
Guys/Gals

I have been given the task at work to ' Sort out ' the emergency lighting. I am new to the job and have little experience as an electrician, but need to do a good job on this one ( first impressions go far! )

I have 2 buildings to get through, 18 floors on each.
Some floors have all lights on, including luminated emergency signs, some floors dont have any luminated signs on. Is there a regulation stating that all emergency lights should be on at all times? One of the floors i had a quick check over didnt have any LED lights to show where the emergency lights are, is this a regulation that needs to be looked at?

Thanks for any other advice that could be of any help!

As some of the guys below have responded already, BS5266 is the base "guide" you need. Emergency lighting is covered in that Standard in various parts, depending on what your involvement is, and most likely, Part 1.

However.

As with fire alarms, the need for emergency lighting, type and duration should ALL be covered off in a Fire Risk Assessment - that is, should give you a base to work from. There is, after all, little point in maintaining any system which doesn't do the job it was intended to in the first place.

There are several types and durations of emergency lighting - and NOT ALL of them are such that you will see LED indicators on the light fittings - especially if what you are looking at is either an inverter controlled, or central battery system. It might be an idea to first ask for ANY paperwork at all which may exist for these systems.

As for illuminated exit signs......oh boy. There is NO REQUIREMENT AT ALL for illuminated exist signs. The requirement is for a BS5446 sign which can be seen in emergency conditions - and therefore, a photo-luminscent sign will do the job as well, and cheaper than an illuminated sign.

An illuminated sign (that is an emergency light fitting with a decal applied, or purpose built to be a sign which is lit) IS NOT AN EMERGENCY LIGHT FITTING. IT WILL NOT PRODUCE THE REQUIRED LIGHT OUTPUT TO QUALIFY AT THE SAME LEVEL AS A FITTING WITHOUT A DECAL APPLIED.

Safety and escape Signage is strictly a Fire Risk Assessment matter, and NOT an emergency lighting matter.

So, with any emergency lighting system, in simple terms, you are inspecting to ascertain:

Light level - needs to be a minimum of 1 lux along the centre of the escape route at all points. Emergency light fittings come with ICEL calculation tables which tell you how the light will spread from the fitting, and how close together they need to be to produce the desired output level.

Of course, light level applies only after you have confirmed that escape routes are properly defined.

Lights also need to be placed at each change of direction, or level, over and above the light level requirement.

Duration - the system is rated at the duration state don the light fitting. Therefore, each fitting (if self contained) needs to be duration tested for the time indicate don the fitting - typically three hours.

For central battery systems, the duration rating will be on a plate either by the batteries or on the control panel, and the same with inverter systems - which may be central, or may be installed per fitting.


Realistically, it seems to me that your first best bet is going to be to cut out lighting ways on each floor, one at a time, and see what stays on - and then get your head above the ceiling to find out what SHOULD be on - unless some kind soul left you a plan.

Without disrespect to any of the guys out there, the above are reasons why emergency lighting is not really run of the mill work - it follows similar levels of requirement to fire alarms. And that's without mentioning that compliant emergency lighting is generally NOT wired using twin and earth cable.
 
have a word with your local wholesaler. Some lighting companies they will deal with will do lighting designs for this sort of scenario. If all goes wrong it's their indemnity that you'll be claiming on.
 
have a word with your local wholesaler. Some lighting companies they will deal with will do lighting designs for this sort of scenario. If all goes wrong it's their indemnity that you'll be claiming on.

Well said, Dunc.

It is NEVER a bad thing to ask the equipment manufacturer for design assistance - it's THEIR specification the equipment is performing against, after all, and if they're claiming it has compliance with the standard......they SHOULD take the risk on design too if their kit is making up the system.
 