Guest viewing limit reached
Spudnik
Now then,
Scenario....
Big shop, 5 internal lighting circuits.
EM's installed as per spec, with a few on each circuit.
LE lighting used with EM conversion packs used.
How would you go about installing a test switch for EM's?
Would you
a) install key switch for each EM pack next to the converted fitting, bearing in mind that the lighting is all L/E recessed,
b) test switch at DB powered from respective circuits,
c) not bother and just use circuit MCB's as the testing will only be done during daylight hours.
Just after opinions, as i have already done it and would be interested to hear others P's.O.V
Ta
how are the 5 lighting circuits split up? 5 seperate floors of a couple per floor? whats the location of the c.u?
Its in a shop and so all on one floor and split due to loading.
CU in under stairs walk in cupboard:)
option b would be the best way, having an emergency lighting contactor in at the cu
Done this boat loads and would normally take the feed to the switch then take a 3-core and earth up to the lighs so you can pick up emer as well as normall lights
Emergency Lighting.
Spudnik,
Doomed,