Emergency stops for LAB sockets | on ElectriciansForums
Discuss Emergency stops for LAB sockets in the UK Electrical Forum area at ElectriciansForums.net
fareham
I have been tasked with installing emergency stop buttons at the doorways to a few labs, so in an emergency they can hit the stop button and it will kill the power to all the sockets in the room.
Now the problem is they are all rings with the DB's some distance away. Had they been radials t would be easy, simply break the circuit as it comes in and wire through the EMG Stop, job done, has anyone had a scenario like this and overcome it?
Would the only way be by mounting something at the DB Like a 4 pole relay, wire the ring from the MCB straight into it, and control that by an EMG Stop button sited in the circuits room, wired from the DB where the sockets are?
Or possibly catch the ring as it enters the room and mount the relay there if the legs close together, as some rooms are Dado trunking on walls.
Any advice/ help?
Stick a contactor in where the ring enters the room, and wire the stop button to the coil, I would recommend a stop button with a key facility, that way a competant person will have to use a key to open it and would do so only if it is safe to do so.
Yes, i was thinking installing it where it enters the room and use stop button to coil on N/C contractor but its highly unlikely the two legs of a ring will be next to one another will probably go to either end of the socket runs which are quite large areas.
I also suppose for the purpose a 2 pole N/C contractor would suffice just cutting the two live cables?
I would not use separate poles of a contactor to break two legs of a ring separately, and certainly not break only the line in that way. If the contact resistance rises it could interfere with the current sharing, and if one contact went high resistance you would not know about it because the sockets would carry on working. I would prefer to see the control cable run back to contactor adjacent to the DB and the ring moved from the DB into it.
If the cables run to the rooms together, with suitable checks and precautions you could possibly parallel them and create a lollipop circuit so that the contactor could go in the room.
As far as re-energising method etc, this needs to follow from their risk assessment which should show what specific risks they are trying to minimise, and how the E-stop is intended to minimise them.
What if the lights are on the same DB? And the contactor coil circuit?
Also surely he wants a separate stop for each room?
I thought the original post said ALL THE SOCKETS are fed from the same DB if they are not the fit a new DB just for the sockets and control that one via a contactor
Reply to Emergency stops for LAB sockets in the UK Electrical Forum area at ElectriciansForums.net
If it's going to be an emergency stop and not just a stop, then other factors come into play depending on what sort of machines the emergency stop...
By retired electrician, I mean that I have retained my ticket but no longer do installation work. Thanks for the clarification. I missed that it...