Hi guys, working on an emersion today. Had 230 volts at the switch and 230 leaving the switch but when used meters across neutral and sink/bath it only read 20volts. Any idea what the problem may be? Cheers lads
 
Do you mean immersion water heater ? if so then the thermostat need to be checked along with the heater element so the next question is it a standard uk set up or is it one of these french megaflow systems
 
Think you'll find that the immersion is dual element, sink/bath and the switch marked accordingly.
Have you inserted a link between the live load out and the common of the two way ?
 
Last edited by a moderator:
Assuming the above post about dual.

If it's got 230v live in to the switch measured L to N and L to E, then L N and E must be good.
If it's 230v L to E but not 230v L to N then the incoming neutral has failed somewhere else, maybe at the MCB/ fuse board / RCCB /RCD.

If it's got 230v live out of the switch on either bath and or sink, measured L to E but not L to N then the Neutral part of the switch has failed.
Confirm the above by measuring across the neutral in and neutral out at the switch, you'll have 210v (ish)
 

Reply to Emmersion Heater in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
780
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
789

Similar threads

  • Question
Fantastic thanks Freddo that last photo confirms all your suggestions so I’ll get back over and remove the links and test. Thanks again!
Replies
4
Views
1K
D
  • Article
DHW supply from Vaillant turbomax 828e Hi, We have a combi boiler supplying dhw and c/h to our 4 bed, 2 bath house. The boiler is in a cupboard...
Replies
0
Views
165
diddlepara
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top