I've been testing on a commercial installation where all lights are sat in the ceiling grid and then flexed back to a central LCM. One LCM per room/area.
The LCM is then flexed into a klix plug+socket on a conduit.
Now we're being asked to test r1+r2 and Zs at the klix socket. (as it's easier and were up against it at the minute) But this is not taking into account the additional resistance of the flexes away to the light fittings. So it's not truly end of line is it?
Surely I am right when I say the measurements should be taken at the last fitting? I know i am right really, I just come to get feedback and other opinions from you guys..