I've been testing on a commercial installation where all lights are sat in the ceiling grid and then flexed back to a central LCM. One LCM per room/area.
The LCM is then flexed into a klix plug+socket on a conduit.

Now we're being asked to test r1+r2 and Zs at the klix socket. (as it's easier and were up against it at the minute) But this is not taking into account the additional resistance of the flexes away to the light fittings. So it's not truly end of line is it?

Surely I am right when I say the measurements should be taken at the last fitting? I know i am right really, I just come to get feedback and other opinions from you guys..
 
You only need to test up to the LCM then.
These set ups, usually have all the leads the same length.
Disconnect one of the leads to an LCM, then use that as a test lead.
Plug it into the last point on each circuit, and test at the end of the lead.
When you've finished all the circuits, re-connect the lead.
 
The LCM is fused, that fuse protects the circuit down stream from it.
Your Zs are required to confirm that the Circuit Protective Device will operate in the specified times.
It's the same as with an FCU.
 
We only test to LCM , when you test a ring do you test the appliances plugged into it?

No because the devices plugged into it are always going to be random. But the lights in the ceiling are going to stay. And if anyone gets a belt, then most likely that is where it will be.

I get the point though about the fuse in the LCM protecting everything downstream. That hadn't occured to me as I'd forgotten it was there.
 

Reply to End of line.. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
307
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
830
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
929

Similar threads

Interesting question & always gonna get different views on this. EICR testing seems to have changed over the years & not by us the Electricians...
Replies
7
Views
1K
  • Question
No live and neutral at the wall. But that would be the switch live right?
Replies
14
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top