oldtimer

All
I have just changed the CU in my brother inlaws new house he has a 2 bedroom end terrace and there is 4 in the block he has a 3 phase swa cable supply to his house and this supplies all 4 houses in the block so when he gets his extention done next year and then gets the house tested for building control (Scotland) How do you test the main ELI when there is 3 other houses connected to the main cable via 3 16mm earth cable on an earth block. Plus how if one of the other houses were to be tested how would you get around the various other paths to earth ? If you see what I mean.
 
Last edited by a moderator:
I think I see what you mean
Is your train of thought that these others would need disconnecting from the MET in order to measure Ze ?
My opinion would be that they are parrellel paths that could exist on the earthing system of any estate except that the actual connection of these properties are in your visible location
When we measure Ze it doesn't exclude these parrallel paths in Tn systems in all other situations
Either inquire off the supplier what they declare as the Ze for that area or take a reading and ignore these other main earths
 
Last edited:
thanks for the reply
I could disconnect the other earths to get a "true" reading but what reading would i get if his house was one of the other 3 ie you cannot tap on the door of the other 3 houses to see who has the 3 phase supply and distribution fuses in their house.
Ironically i am in that position as the house 3 doors down has this set up. o hum
Also forgot to ask is this set up common across the country or only in scotland
 
Last edited by a moderator:
thanks for the reply
I could disconnect the other earths to get a "true" reading but what reading would i get if his house was one of the other 3 ie you cannot tap on the door of the other 3 houses to see who has the 3 phase supply and distribution fuses in their house.
Ironically i am in that position as the hous 3 doors down has this set up. o hum
Also gorgot to ask is this set up common across the country or only in scotland

I would test Ze in the property that concerns you as it would be totally impractible to isolate everyones supply to test at true origin. Yes you will have parallel paths but no way round it.
 

Reply to end terrace house in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
267
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
754

Similar threads

As per above from Dave. Swap to a 63A outlet and problem goes away. What gets plugged into it is not part of an inspection.
Replies
20
Views
2K
Your electrician shouldn't be doing anything to the cutout, that is the property of the electricity supplier and they make the connections to it...
Replies
3
Views
950
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top