I have a problem with a power ring main circuit. I have 'end to end' readings for Neutral and CPC but an open circuit reading for the Line. However, when I crossover Line and CPC and take readings at all the sockets, the readings are fine. I don't understand, if there is a disconnect somewhere in the Line then that should affect the readings when I do the crossover. Any ideas? Thanks.

Nick
 
When you cross connect the wires it is the equivalent of creating a ring and placing your test probes at opposite ends.

The readings should always be about the same for sockets on the ring, because as one probe switches point the other moves to the exact opposite end i.e. when when probe is at 12 o clock, the other is at 6 o clock if that makes sense :)

If the ring has a break then there will be only one circuit path between each test probe, that will consist of some earth conductor and some line conductor. As the probes move round the proportion of earth and line conductor will change, but may only result in a slight change in readings.

Think thats right anyway
 
Hi,

I have a problem with a power ring main circuit. I have 'end to end' readings for Neutral and CPC but an open circuit reading for the Line. However, when I crossover Line and CPC and take readings at all the sockets, the readings are fine. I don't understand, if there is a disconnect somewhere in the Line then that should affect the readings when I do the crossover. Any ideas? Thanks.

Nick

What were the measured value for the end to end reading for neutral and CPC, and what were the reading at each socket when you crossed over Line and CPC.

Did you find the break in the Line
 
The end to end readings were Neutral 0.27 and CPC 0.35, the crossover readings at each socket were approx 0.3, give or take 0.1.
I removed every single socket face on the circuit and checked the Line connections but found nothing amiss. Not sure what else to try. I don't want to leave the circuit as it is.
Flukey, I moved on to the crossovers to see if that would help me work out the issue, didn't help, so trying to find out here.
 
The end to end readings were Neutral 0.27 and CPC 0.35, the crossover readings at each socket were approx 0.3, give or take 0.1.
I removed every single socket face on the circuit and checked the Line connections but found nothing amiss. Not sure what else to try. I don't want to leave the circuit as it is.
Flukey, I moved on to the crossovers to see if that would help me work out the issue, didn't help, so trying to find out here.

Before try the following test to find the broken Line I would do an insulation test between live conductors and earth, in case insulation has been damaged to earth

As the Neutral and CPC were ok use ever of these rings, goto the CCU and take either the CPC or neutrals from there terminal I would take the neutral out and connect one of the broken Line conductors to the neutral, then test between L-N at each outlet until you fail to get a reading, mark that socket, return to the CCU and remove the line, then connect the other line to the neutral and test the other socket outlet, until you do not get a reading, I suspect that the break may be between 2 socket, there could be a JB under the floor, I had nails blow open the Line, had a similar problem in May this year, client had put a shelf up in the kitchen and damaged the Line.

Let us know how you get on.
 
The end to end readings were Neutral 0.27 and CPC 0.35, the crossover readings at each socket were approx 0.3, give or take 0.1.
I removed every single socket face on the circuit and checked the Line connections but found nothing amiss. Not sure what else to try. I don't want to leave the circuit as it is.
Flukey, I moved on to the crossovers to see if that would help me work out the issue, didn't help, so trying to find out here.
have you tried breaking down the ring and testing each way :confused: if you got no continuity you gotta find that break
 

Reply to End to End problem with Line wire in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
745

Similar threads

I did consider this but ended up going with this one. I wired it inline with the lives and works great.
Replies
7
Views
551
  • Question
He is after the four options for 1 and 2 of the multiple choice exam, probably optimistic someone will know this. Your question 3 in incomplete to...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top