End to end test r2 greater then r1 & rn | on ElectriciansForums
Discuss End to end test r2 greater then r1 & rn in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
J
jamminuk
Hi,
Just a quick one, tested a ring today after new install, 2.5 singles in conduit. When i cam to do the end to end test i had these results:-
Flat ring
r1 = 0.44 rn = 0.44 r2 = 0.36
Kitchen ring
r1 = 0.23 rn = 0.23 r2 = 0.15
Not sure why the r2 was lower on both circuits if all are the same length and csa, are these reading acceptable?
Ben
Archy - That did cross my mind, however the kitchen ring is in mini trunking (forgot to mention) and the flat ring in metal conduit. hmmmm
Murdoch - That did also cross my mind but cant think where these paths could be, especially in the kitchen ring, but i suppose somewhere along the line it must be
Thanks guys
Not really acceptable for an initial verification.
You should ensure that there are no parellel paths and re-test.
This is one of the reasons why some tests should be conducted during construction rather than after construction is completed.
Reply to End to end test r2 greater then r1 & rn in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
6K