The point is, Zs is not always indicative of the conformity of the CPC size.
Here's an example.
6mm Line, 1.5mm CPC, fed from a 32A CB with a 30 metre length.
Ze assumed to be 0.35,
Zs = Ze + (R1 +R2)
R1 = 3.08m ohm/m x 30, R2 = 12.1 mohm/m
R1 + R2 = 0.45 ohms, + Ze of 0.35
gives a Zs of 0.90, - well under the limit of 1.44 (non-corrected).
Anyone who hadnt inspected it properly, and just did a live Zs test, would assume that to be a good reading, and tick it off as a pass.
Now we have been called back as there has been a short circuit at the switch, and the cable has burnt through.
We go back, see the 1.5mm CPC, then do the PEFC test, and find there is a 500A earth fault current.
Looking at the tables, we find the CB will trip in 0.1 seconds.
So why did it burn?
Do the adiabatic, and we see why:
Fault current 500A, disconnection time 0.1s so doing the calculation 500x500 x0.1 square root answer, divide by 115, gives an answer of 1.37 sq mm.
Thus showing the CPC is too small for the circuit thermally , but as above, Zs would pass easily.
OK, the CPC would probably not melt, but, it is going to get hotter than recommended, so should be avoided, hence why it is not good enough to just rely on the tested Zs result to pass a circuit as acceptable.