Do any of you guys test for erroneous connections when you are doing your IR tests?
 
An erroneous connection is a physical connection between 2 circuits.

Have you ever been in a situation were you have opened a breaker and the load side is still live?
An example of this could be 2 radial socket circuits with the phase linked between the 2 circuits.
2 phase conductors fused together inside containment due to heat or installation methods i'm sure you get my drift by now.

The reason i posted this is because i found such a situation yesterday and luckily the guy that i learnt from told me always to do this test while carrying out the IR tests.

The test procedure is as follows.

IR tester on 500V

Main switch open all MCB's closed except for the first one that you are going to test which should be open.
One probe on to MCB supply bus bar and 2nd probe on to load side of breaker that was left open.
Apply 500V.
Repeat the process by opening the next MCB and apply test voltage to load side.
Repeat for all breakers.
 
Last edited:
from that post, sintra, i assume a zero or low reading will tell you that you have got a cross connection, if i am reading it correctly.
 
Hi Sintra, wouldn't safe isolation with an approved voltage tester be another way of doing the same thing?

Or do i go the to the back of the class with Ezzze ;)
 
Last edited by a moderator:
Hi Sintra, wouldn't safe isolation with an approved voltage tester be another way of doing the same thing?

Or do i go the to the back of the class with Ezzze ;)
up to a point. if there was a short, you'd read 230v, but if insulationn breakdown, your tester might not show a reading.
 
I do ever since being confronted by a "downstairs ring" interconnected to an "upstairs ring".:confused:
Turned out that some bright "spark" working for a kitchen unit company (Moben) had decided not to run a new separate ring for the kitchen. Instead he connected the new kitchen sockets ring extention into one leg of downstairs ring and the other end into a leg of the the upstairs ring, bridging both rings.:mad:
 
Last edited by a moderator:
Hi Sintra, wouldn't safe isolation with an approved voltage tester be another way of doing the same thing?

Or do i go the to the back of the class with Ezzze ;)

Safe isolation would be fine if you are a competent person going to work on a circuit. But Mr DIY goes to change an accessory he knocks off breaker for the circuit and proceeds to get a shock. If you or I have done work and issued a cert for say a cu change I think we could end up in the big house.


Sent from my iPhone using Tapatalk.
 
I always do it when i carry out an inspection especially when working on old houses or houses where Mr DIY come in and says i put that socket in whilst grinning like a cheshire cat , found one last week whilest doing a CDU up grade carrying out some initial tests as i always do ,ring and immersion heater supplies crossed so like been said its ok if professionals do are working on it they can spot it

its like anything realy test before you isolate and after you isolate ,test test and test again ,have seen so many people say its still live after theyve touched a live part
 

Reply to Erroneous connections in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
369
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
931
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Unless the circuit is new or has recently been tested/certified by a.n.other, I'm not sure how you prove the circuit is 'safe' to connect to...
Replies
1
Views
277
There is a lock on it, press the test button down and press the lock button, the symbol will appear on the screen in the middle right hand side...
Replies
5
Views
489

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top