We installed a PV system approx. 18 months ago which has recently started showing an event number 35 in wet weather conditions which according to the manual is a ground fault.
The system is a floating class 2 array so presumably we cannot have a ground fault.
We have tested the system during dry operating conditions and again whilst the event is displayed and the results were as follows
DRY conditions, no event
Voc, String 1 - 320.1V String 2 - 320V
Isc, String 1 - 1.8A String 2 - 1.8A
Sun 86W/m2
WET conditions, event number 35
Voc, String 1 - 342.2V String 2 - 342.1V
Isc, String 1 - 1.6A String 2 - 2.5A
Sun 88.8W/m2
Is the fault likely to be as simple as water ingress into one of the connections? We would like to be sure before we go to the expense of getting back onto the roof and remaking all connections.
Any help or advice would be much appreciated.
Cheers
We installed a PV system approx. 18 months ago which has recently started showing an event number 35 in wet weather conditions which according to the manual is a ground fault.
The system is a floating class 2 array so presumably we cannot have a ground fault.
We have tested the system during dry operating conditions and again whilst the event is displayed and the results were as follows
DRY conditions, no event
Voc, String 1 - 320.1V String 2 - 320V
Isc, String 1 - 1.8A String 2 - 1.8A
Sun 86W/m2
WET conditions, event number 35
Voc, String 1 - 342.2V String 2 - 342.1V
Isc, String 1 - 1.6A String 2 - 2.5A
Sun 88.8W/m2
Is the fault likely to be as simple as water ingress into one of the connections? We would like to be sure before we go to the expense of getting back onto the roof and remaking all connections.
Any help or advice would be much appreciated.