Hi all, just having a read through the regs and code of practice on car chargers. Where it stipulates the use of RCD's "for charging points" eg 722.531.3.1, is that referring specifically to the charge point it's self, ( and the fact that protection may be contained with the unit) rather than the circuit supplying it, which depending on installation, may not require RCD protection. I'm guessing it is, as the COP has a note 5.6.2, mentioning issues over selectivity between protective devices for the circuit, and prietive devices within charging equipment.
 
I wouldn't worry too much about selectivity between protective devices on a circuit feeding a single device.
The reason for selectivity is to minimise nuisance (and possible danger) if an upstream device switches off power to a group of circuits instead of a lower rated device switching off power to just the faulty sub circuit.
I the case of an EV charger, if a device detects a fault and disconnects the power, the only effect is that the EV stops charging, whether the device that turns off is upstream or local. No nuisance or danger to any other circuit.
 
I wouldn't worry too much about selectivity between protective devices on a circuit feeding a single device.
The reason for selectivity is to minimise nuisance (and possible danger) if an upstream device switches off power to a group of circuits instead of a lower rated device switching off power to just the faulty sub circuit.
I the case of an EV charger, if a device detects a fault and disconnects the power, the only effect is that the EV stops charging, whether the device that turns off is upstream or local. No nuisance or danger to any other circuit.
To be fair, the COP does say, in effect, not to worry about it if it can't be achieved
 
To be fair, the COP does say, in effect, not to worry about it if it can't be achieved
sometimes in it unavoidable, the circuit requires RCD protection at source, irrespective of what is in the charger. if the charger is the only circuit from the rcd/rcbo then there is no inconvenience in event of a fault, if anything its a fail safe and back up as its not unheard of for the built in RCM/RCDs on some devices to not operate.
 

Reply to EV chargers and RCD protection in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
953
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
957
That's not really 'openly stating' if you have to ask - because of course, most people simply won't ask.. Which must happen all the time - if a...
Replies
14
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top