EV charging point query | on ElectriciansForums
Discuss EV charging point query in the Electric Vehicles Advice Forum area at ElectriciansForums.net
Andy C
Wirral
I have a nice job on in a few weeks which includes wiring up a solo chargepoint EV point. The pod doesn’t have its own RCD like Rolec do.
I am rewiring the house and intended to use either a type A RCD or RCBO.
As they also detect small levels of DC leakage.
I use BG consumer units but I don’t think they do them.
What are the views of changing one of the general type AC RCDs for another type A make or do I go for a whole new board.
Thanks in advance.
The manufacturer suggests using a type B RCD.
It may be best to install a separate enclosure with a type B RCD to protect the EV point.
To install a different manufacturers RCD in a BG board is not really ideal and definitely more prevalent in the current regs as a non permitted option.
The manufacturers installation instructions are 2017 and out of date, they apparently quote regs that don’t exist. They suggested that the pod,point could be fitted using the TNCS system. Whereas I understood it had to be a TT Island in this case.
I will probably go for a different board as I wanted to keep the board neat with the circuit supply in the dB.
The Rolec stuff looks much better but the client has already bought the charge pod.
The best source of rcds or rcbos for ev chargers is rolec. They are between 15 and 20 quid depending which wholesaler you go to. Give them a call and they will give you the product code to use in the wholesalers.
Can put one in an enclosure adjacent to cu to supply the charger fed via a unprotected mcb. Not familiar with chargepoint as i only install rolec or evbox. Both have integrated protection.
Out of interest what mcb do they recommend for the chargepoint units?
Some makes recommend type c over type b.
Thanks in advance.
Hi there
In the new wiring regs you can’t swap and change the breakers or RCD with different makes unless you become the “manufacturer “ and can certify them as fit for purpose as mixed suppliers.
You will have to buy a full board by another manufacturer with type A installed such as Hager do as standard now or install a separate board with main switch and an rcbo
Reply to EV charging point query in the Electric Vehicles Advice Forum area at ElectriciansForums.net
Tesla & Porsche chargers come with a commando adapter that allows them to charge at 32a, if that’s the car in question. Which with clipped direct...
Can imagine getting a 6mm through an existing conduit of 22mm with a cable already in might have some challenges in it’s self. Obviously not been...