Problem arisen with a solar pv system installed in December 2011.
Eversolar 4000TL connected to 16 250W Suntech panels (1x string)
Worked fine until 3 weeks ago where a problem has developed in bright sunshine, inverter makes a loud clonk and cuts out.
Reads error code: UAC failure, reconnection pac = 0.0w
Inverter datasheet states: max DC current 680 and MPPT voltage range: 115 - 550.
suntech panels datasheet: optimum operating voltage 30.7, Open circuit voltage: 37.4.
Suppliers have said that it should have been one String as the max MPPT is 550 and the voltage running through one string could be over 600V (not sure where they're getting that number from)
Are they correct, should it have been one string? I find that hard to believe usually if that's the case the inverter has an error message immediately, not 18 months down the line. Second question, is the inverter now damaged, or will switching it to two string fix the problem?
Thank you in advance for your help!
Problem arisen with a solar pv system installed in December 2011.
Eversolar 4000TL connected to 16 250W Suntech panels (1x string)
Worked fine until 3 weeks ago where a problem has developed in bright sunshine, inverter makes a loud clonk and cuts out.
Reads error code: UAC failure, reconnection pac = 0.0w
Inverter datasheet states: max DC current 680 and MPPT voltage range: 115 - 550.
suntech panels datasheet: optimum operating voltage 30.7, Open circuit voltage: 37.4.
Suppliers have said that it should have been one String as the max MPPT is 550 and the voltage running through one string could be over 600V (not sure where they're getting that number from)
Are they correct, should it have been one string? I find that hard to believe usually if that's the case the inverter has an error message immediately, not 18 months down the line. Second question, is the inverter now damaged, or will switching it to two string fix the problem?
Thank you in advance for your help!