What does this question prove then??
Depending on the test Zs value it will be clear that there is a potential problem within that circuit.The only problem here appears to be in the initial selection of the OCPD,and as it is a 3871 device chances are it is an old install and complied at the time. Are you still going to say ...all's fine because i have a cover-all RCD in circuit, that is basically there to afford additional rather than the ONLY or SOLE means of earth fault protection on TN systems!! It isnt the only means of earth fault protection,the mcb will still trip but not in the required 0.4s,which the RCD will take care of......on many circuits an MCB is the ONLY or SOLE means of earth fault protection,never hear you knocking that.
Does nobody ever check these day's, as to WHY a circuits ADS Zs value no longer complies?? As RCD protection can never be the sole means of protection on a newly installed TN circuit, the offending circuit must have complied at one time... Or are we now actually installing circuits these day's, that rely on a RCD's Zs protection from the word Go??It's an EICR on an older installation....likely there is nothing wrong with the circuit,just the initial choice of OCPD,which I say again,likely complied at the time