Sb8389
Nottingham
hey guys
we have done an EICR on a 2 bedroom bungalow, the supply is a 25mm 4 core 3 phase SWA to the property, it is supplied from 80amp fuse.
although it is speculative as the cable is underground we reckon the distance is around 600m :fearscream:.
it has being installed around 10 years and no evidence of thermal damage or any concerns of equipment not functioning correctly as per tenants.
the Zdb is 1.89 so disconnection time is not achieved either. the volt drop is around 72volts based on potential load of 80amps.
there are no 3 phase circuits in the installation but it is fully electric so it does have 6 panel heater and an electric hob/oven.
what code would you give based on the voltage drop allowance not being achieved.
Reply to exceeding voltage drop in the UK Electrical Forum area at ElectriciansForums.net
That looks like a Metrel display (I have one), they have a permanent 3 wire display that measures the three combinations so I would say that’s a...
Surely that will depend on what is connected to it. And the nominal voltage between phases is 400V (+10%/-6%).