Excess bare live conductor at terminations - code? | on ElectriciansForums

Discuss Excess bare live conductor at terminations - code? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

W

WDMDL

When wiring is terminated in a shoddy manner at a socket outlet and there is about 6mm of bare conductor exposed at the L and N terminals, what do you code it?
Personally I think a 2 is appropriate as it may give rise to danger - not a 1 as you can't touch it, but certainly more serious than a 4

Simon.
 
WDML if this a terminal in a socket. or a light or a CU which in normal use would not have any mechanical stresses like vibration on it why would you deem it is in need of improvement to a degree that it could become dangerous.

Yes a motor or a piece of equipment that moves you could if you felt there was a chance of bare conductors touching due to that movement code it but I would never code it a 2 as you are then most likely to deem the installation unsatisfactory.

If you want to code it then perhaps a 4 for 134.1.1 for workmanship
 
Code 2 Requires Improvement

This code is to be used to indicate that the observed deficiency requires action to remove potential danger.

Taken from the ESC guide as a reference

We are saying that if the insulation of a conductor as been stripped so far at a screw terminal that there is bare conductor showing, and if this is encased in an enclosure that requires a tool to access it, and there is no influences of vibration or mechanical stress on the cable it is a danger, to who?
 
OK thanks Malcolm, makes sense... just thought about possibility of arcing to back box etc


Oh, and the installation was unsatisfactory anyway... Someone had changed the BS3036 fusebox for a BS3871 consumer unit - many many moons ago - but didn't bother to do some essentials like extending the CPCs to reach the earth busbar - they were just left in mid air!
Had to sort those on the spot.

Basically the story throughout the house was the original installation was sound, but let down by poor workmanship on the additions and alterations.

Not seen one as bad for a while - but I have got the remedials :)

Simon.
 
Last edited by a moderator:

Reply to Excess bare live conductor at terminations - code? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
897

Similar threads

  • Question
There is no homework, and I'll never see these photo again.
Replies
3
Views
608
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top