explain this..... | on ElectriciansForums

Discuss explain this..... in the UK Electrical Forum area at ElectriciansForums.net

H

Hawk

So on the test results (see pictures) it states TT system, earth rod, however from the picture of the supply it can be seen that there is a suppliers earth which looks like tncs to me.
 

Attachments

  • [ElectriciansForums.net] explain this.....
    IMAG1380.jpg
    150.3 KB · Views: 222
  • [ElectriciansForums.net] explain this.....
    IMAG1074.jpg
    62.2 KB · Views: 239
It's possible that the earth has been connected to the head at some point in time after the original installation was carried out.

Is there anything in the installation which would mean that a PME earth connection cannot be used?

Is the rod actually there?
Does the rest of the certificate make sense?
 
Update.... Got called out to same job as outside lights where causing the rcd, that covers the majority of the premises, to trip. Found lose neutrals in the lighting circuit which seems to be the cause as they have been fine for 2 days now. Anyway while I was there I carried out a Ze and got a result of 0.13ohms. I would therefore say that it is tncs system.
Now that that's been determined what would your thoughts be on doing away with the rcd covering the whole board and use individual rcds? So as when a fault develops the whole board won't trip off.
 
It's a commercial installation. Looks as if it was originally a TT system that has been upgraded to a tncs system which would make sense given the 0.13ohm Ze. This means I could use single pole rcbos as the neutral doesn't have to be disconnected if a fault develops on a tncs system. Whereas with a tt system both line and neutral have to be disconnected.
 
Update.... Got called out to same job as outside lights where causing the rcd, that covers the majority of the premises, to trip. Found lose neutrals in the lighting circuit which seems to be the cause as they have been fine for 2 days now. Anyway while I was there I carried out a Ze and got a result of 0.13ohms. I would therefore say that it is tncs system.
Now that that's been determined what would your thoughts be on doing away with the rcd covering the whole board and use individual rcds? So as when a fault develops the whole board won't trip off.

Were the readings the same with Ze & Zpn?
 

Reply to explain this..... in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
295
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
802
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
838

Similar threads

  • Question
I'm assuming the cable will have to be cleated well to hold it in place anyway, as a stuffing gland ain't going to hold it tight like a SWA gland...
Replies
10
Views
705
  • Question
and you Dave
Replies
9
Views
959

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top