brucelee
-
hi everyone,
got my 2391 on thursday getting a little nervous now anyway,
I want to ask when asked to explain how to do a IR test on a existing circuit
how do you word the safe isolation part do you have to explain the whole procedure as time is short or would it be ok for the following
. Seek permission to isolate the supply, warn people of the test
. locate, safely isolate the supply for the circuit,lock off,label, CBs off
. remove lamps ,disconnect voltage sensitive electronic equipment or linked out to prevent damage
. select a Insulation resistance ohmeter
. confirm calibration, condition and leads to gs38, batteries ok and functioning
. Set to Mohm scale at 500v.d.c.
. at the db test insulation resistance between Line + neutral, operate two way switches, record result
. then test between lives ,operate two way switches, record result
. Min bs 7671 value 1.0Mohm but if lower than 2.0Mohm further investigate as may be a latent defect
. replace lamps and reconnect any electronic equipment
. reinstate supply
or should i go into more detail for the safe isolation part
any help gratefully appreciated for the testing between lives and then live to earth should i put
between line to neutral operate two ways further test record value
then line and earth operate two ways further test &
then neutral to earth record lowest value from these
sorry but i am not sure as i have exam suucess and only explains for a new circuit
I also have Cristopher Kitcher practical guide to inspection and testing and his version different again as follows
. Ensure safety whilst test is being carried out
. Isolate circuit to be tested using safe isolation procedure
. remove all lamps
. if removal of lamps is difficult or flourescent / transformers are on the circuit open the switches controlling them
.Isolate or bypass all electronic equipment and equipment tha tmay be damaged or give false readings
. Use an insulation resistance tester set on 500vdc
. ensure Instrument accurate and operate the istrument with the leads together and then apart to ensure correct operation
. test circuit between live conductors
. Operate two way any two way switches controlling points where lamps have been removed
. join live conductors together and test between them and earth
. operate all two way switches
. the insulation resistance should be above 2.0Mohm if it is less , then further ivestigation must be carried out as ther may be a latent defect may exist
. it says a insulation resistance of 0.5Mohm is acceptable in some cases this is wrong unless selv
Replace all lamps and remove any shorting links used
.leave circuit safe and operational
any advice would be a big help thanks
got my 2391 on thursday getting a little nervous now anyway,
I want to ask when asked to explain how to do a IR test on a existing circuit
how do you word the safe isolation part do you have to explain the whole procedure as time is short or would it be ok for the following
. Seek permission to isolate the supply, warn people of the test
. locate, safely isolate the supply for the circuit,lock off,label, CBs off
. remove lamps ,disconnect voltage sensitive electronic equipment or linked out to prevent damage
. select a Insulation resistance ohmeter
. confirm calibration, condition and leads to gs38, batteries ok and functioning
. Set to Mohm scale at 500v.d.c.
. at the db test insulation resistance between Line + neutral, operate two way switches, record result
. then test between lives ,operate two way switches, record result
. Min bs 7671 value 1.0Mohm but if lower than 2.0Mohm further investigate as may be a latent defect
. replace lamps and reconnect any electronic equipment
. reinstate supply
or should i go into more detail for the safe isolation part
any help gratefully appreciated for the testing between lives and then live to earth should i put
between line to neutral operate two ways further test record value
then line and earth operate two ways further test &
then neutral to earth record lowest value from these
sorry but i am not sure as i have exam suucess and only explains for a new circuit
I also have Cristopher Kitcher practical guide to inspection and testing and his version different again as follows
. Ensure safety whilst test is being carried out
. Isolate circuit to be tested using safe isolation procedure
. remove all lamps
. if removal of lamps is difficult or flourescent / transformers are on the circuit open the switches controlling them
.Isolate or bypass all electronic equipment and equipment tha tmay be damaged or give false readings
. Use an insulation resistance tester set on 500vdc
. ensure Instrument accurate and operate the istrument with the leads together and then apart to ensure correct operation
. test circuit between live conductors
. Operate two way any two way switches controlling points where lamps have been removed
. join live conductors together and test between them and earth
. operate all two way switches
. the insulation resistance should be above 2.0Mohm if it is less , then further ivestigation must be carried out as ther may be a latent defect may exist
. it says a insulation resistance of 0.5Mohm is acceptable in some cases this is wrong unless selv
Replace all lamps and remove any shorting links used
.leave circuit safe and operational
any advice would be a big help thanks