Hi all back again needing more advice.
I've included some photos. Basically customer has asked me to supply and wire outhouse. Unfortunately as consumer unit is at front of house there's no real possibility of supplying on own circuit. The outhouse will have about 3 x double sockets and couple of lights. The thing that concerns me over the adequacy of supply is that customer would like a heater in here and also a socket for a heater in the garden....a 13 amp spur is not going to suffice in my mind. As can see from photos the only possible route can see is come from one or the two ring sockets in kitchen. To make things more awkward these sockets back onto an outside toilet ? see photo. The outhouse is about 7 metres from here. Any neat feasible point in right direction be appreciated. Have heard others suggesting a ring lollipop.....So could potentially extend ring into a large junction box opposite socket and in toilet and then could run some 6mm 3 core around the toilet, punch outside into another junction box ? then take 6mm armoured either to outhouse or preferably to garden socket first (is this feasible?) Then on to junction box in outhouse and from here wire a ring for sockets and a spur for lights. Am I missing something really stupid? Does this seem compliant to you? Or is there easier ways?
  • [ElectriciansForums.net] Extending ring to outhouse?
There would be nothing to stop them from plugging these two heaters into the existing rfc, and not overloading.... so let us look at other options here.
1. keep it simple. If you’re going to extend the ring, then extend it. 2x 2.5’s out to the outhouse.
2. Spur it out, but rather than a 13A FCU, make it a 20 or 25A mcb, in a suitable enclosure, giving the option to isolate inside the house and add an RCD if there isn’t one on the circuit already.
3. Is there an unused cooker circuit perhaps you could repurpose?
Are you certain there’s no access to get to CU? Even with limited space under boards, you could push rods from back to front.
Or is it concrete floor?
I would really like to find out from customer the actual load they expect to be using.
Many a time I have been asked for an outside socket “just for the lawnmower”.... then I get to the job, and there’s a lazyspa sitting in its box waiting.
“a couple of heaters” could be 2 at 3kW apiece.
Thanks Little spark that's really helpful. Unfortunately yes solid floors and loads of obstacles to get past for new circuit. I'm considering the option 2 you mentioned. So could potentially use something similar to 2 way CU? Take both my 2.5 ring conductors into top of 25amp MCB. Then use 4mm twin to outside enclosure and take 4mm SWA to outside socket then onto the outhouse. The use of 4mm should ensure not volt drop issues. Thoughts...this seem like a plan
Thanks Matt. Do you mind clarifying why? What would you do in situation like this where no option of new circuit and 13amp spur very likely to get overloaded?
In all honesty I’d probably walk from the job unless I could run a new circuit back to the consumer unit.
Putting a 20/25A MCB protecting a spur off the ring seems like a fairly poor design to me. Quite a large load on a single point on the ring potentially. I personally wouldn’t do it, although I’m sure an argument could be made for doing it.
I mentioned this idea in a thread.
Have a read.
Have a read.
Hi mate
Thanks for that had a good read of it. At this stage I think I'm more inclined to go with a 20/25 amp MCB in an enclosure and take a 4mm to outside socket then down to outhouse
When you think about it, a small enclosure with mcb or rcbo is designed to take anything up to 100A, so whatever the load, it would cope fine.... (OCPD at 32A?)
Cope better than a 13A FCU, even pushing it to full 13A
I get what your saying but going with 32amp MCB in enclosure just pretty much negates the need as have 32 back at board. I am also concerned as others have pointed out if load all on short leg could be overloading this leg of ring. Think I'm more inclined to go with 20/25 atleast then if they really start to overload it would offer some protection
I’d be less worried about the mcb and enclosure than the potential of 25amps at single point on the ring.
Can you explain to me what the likely problems are other than not great design? If 2.5mm rated at 27 amps and supply a 25amp mcb from this how can the cable potentially be overloaded? If draw 25 from outhouse the mcb for outhouse kicks in and if draw 32 in total the one at CU kicks in
Reply to Extending ring to outhouse? in the UK Electrical Forum area at ElectriciansForums.net
If it's buried ducting, have you thought about digging up a section of the buried cable close by, cutting it and pulling in a few extra meters...
One thing you may find is that it will most probably be a 6mm cable and to get two of them in to a terminal may prove to be a stumbling block if...