Sure I am missing something obvious here but having recently gotten into PAT I am confused by some of the extra long extension reels available.
The code of practice for in service inspection & test states clearly the maximum allowable length of extension leads in relations to csa of the core (Table 15.4), and goes on to say that any lead exceeding these limits should be fitted with a 30mA RCD. There seem to be a host of 230v leads on high street sale now that do exceed this and have no RCD protection. Quick example - Masterplug 13A 40m cable reel. This, like many, incorporate a thermal cut-out but no RCD, also after quick ref to BS7671 Table 4F3A fall well short of meeting the voltage drop requirements for both 1.25 & 1.5mm cores.
I feel like I must be missing a trick here. Is it the case that as non statutory regs the codes of practice can be swerved for alternate safe practice?
Confused :dunce2: Any help please...
The code of practice for in service inspection & test states clearly the maximum allowable length of extension leads in relations to csa of the core (Table 15.4), and goes on to say that any lead exceeding these limits should be fitted with a 30mA RCD. There seem to be a host of 230v leads on high street sale now that do exceed this and have no RCD protection. Quick example - Masterplug 13A 40m cable reel. This, like many, incorporate a thermal cut-out but no RCD, also after quick ref to BS7671 Table 4F3A fall well short of meeting the voltage drop requirements for both 1.25 & 1.5mm cores.