don't do much pa testing but noticed a couple of times these show reverse polarity on my megger pat 120 ,but test the pins for continuity and its ok on neutral and earth but no continuity on line,they all work ok ,is the electronics causing problems ?
 
There's a good case to test at both 500V to prove the functionality of the SPD and 250V to obtain a 'normal' value for typical conditions, i.e. without the SPD operating.

If the 500V test returns a high resistance value, then the SPD is not going to be of any use in a real over voltage situation during operation.
 
There's a good case to test at both 500V to prove the functionality of the SPD and 250V to obtain a 'normal' value for typical conditions, i.e. without the SPD operating.

If the 500V test returns a high resistance value, then the SPD is not going to be of any use in a real over voltage situation during operation.
My understanding of how SPDs work, is that every time there is a surge, material is lost.
Eventually, if there are enough surges, the device has to be replaced.
Testing at 500V will reduce the life of the device.
 

Reply to extension leads with surge adaptors in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
300
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
812
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
864

Similar threads

Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
1K
out of interest UK, how do you know what kit is connected?
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top