I have an external SWA cable to install between a garage and a large shed. Does the SWA need to be RCD protected at the Garage end or can it come off its own breaker in the garage CU? The shed end will be conected to a 'garage' CU and have itsown earth spike.
 
Spare way in the garage CU on the RCD side, then all the shed needs is a small CU with a main switch a couple of MCB's.
 
Thanks for the reply - The connection at the Garage CU will be on the Main Switch side of the CU, I have currently in place an RCBO but the problem is that the RCBO in the garage trips befoe the RCD in the shed and I would like to prevent this. Options as far as I can see would be to replace the RCBO for an MCB therefore the shed is relying on its own RCD or remove the SWA from the garage CU and connect via an 'S' type RCD if RCD protection is a requirement for the SWA.
 
I have an external SWA cable to install between a garage and a large shed.
I have currently in place an RCBO but the problem is that the RCBO in the garage trips befoe the RCD in the shed and I would like to prevent this. .


If the earthing system for the garage is TT, then you need to rcd protect the swa to the shed

If you are installing the swa at this time I dont understand how it was determined that
the Rcbo in the garage trips before the rcd in the shed,when it appears that it is not yet installed :confused:
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
External Distrabution Cable Protection
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
3

Advert

Thread statistics

Created
chloebear,
Last reply from
Des 56,
Replies
3
Views
2,595

Advert

TrueNAS JBOD Storage Server

Back
Top