Hi I have a house where in order for the rising main to be earthed, the earth goes around the outside of the property to the fuse box in 10mm cable clipped to the wall at damp proof level. It has no conduit protection. I have recently asked an electrician to upgrade the fuse box and he suggests that the earth is non compliant it is not protected.

Is this the case and what should the cable be protected by?- solid or corrugated trunking?

Any thoughts would be welcome
 
Well I'd personally mechanically protect it if I'd installed it however bs 7671 gives a minimum CSA of 4mm where mechanical protection is not needed for applications such as supplementary bonding and earthing where the conductor is not part of a cable or mechanically protected.
maybe he means the main earthing conductor should be 16mm? Or is the 10mm for the gas or water?
 
It is almost certainly not non compliant but it could be improved. There are many millions of cables installed in this manner. It could most easily be enclosed in conduit though getting the end of the cable available may be inconvenient.
 
Hi I have a house where in order for the rising main to be earthed, the earth goes around the outside of the property to the fuse box in 10mm cable clipped to the wall at damp proof level. It has no conduit protection. I have recently asked an electrician to upgrade the fuse box and he suggests that the earth is non compliant it is not protected.

Is this the case and what should the cable be protected by?- solid or corrugated trunking?

Any thoughts would be welcome
I would also be concerned about a possible bridge of the DPC
 
ideal would be to enclose in black pvc conduit. to do this obviously, to thread it through, entails disconnecting one end. this should be done (in an ideal world) with the installation isolated from supply.
 

Reply to External Earth Cable Protection in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Sounds more positive.
Replies
8
Views
629
Hi Mainline and thanks for the reply. My inverter is only fed from the mains supply over a 4 hour period at night and it does not have any tie...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top