Evening all could anyone please tell me the the maximum ze for tt systems the jobs entail Rec cut out fuse bs88 16a to feed 1x 30 ma rcd fuse spur for feeding socket outlet what should the max ze be please
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss External earth fault loop tt system in the UK Electrical Forum area at ElectriciansForums.net
really 1667 ohms the some are coming up like 180 odd ohms was worried but our manager said it was fine with the 30ma protection and 1667 is what he said we work to I always thought a ze on tt had to be less than 21 ohm
Lets give him 5 mins from now lol
if your circuit is RCD protected at 30mA, the the max. Zs is 1667. bloody joke.
The lower the better but I seem to recall on a regs course that the preferred maximum is no more than 200ohms.
once job is complete do a rcd test with an approved meter if it trips out in the required parameters then ok.
I am still confused my zs can be upto 1667 ohm at the socket but what about my Ra from electrode to incoming supply to spur from rec fuse would tis be 21ohm or 100ohm or 200ohm?
6 Hours later!! lol!!
Another Reg bible basher!! with no understanding of a TT system!!
21 ohms is the max for sub-station earthing and the like, but you'll never see a value anywhere near that high at a sub-station.
The 100 and 200 ohm values that are thrown about by the NICEIC and BS7671 are one almighty joke, and good for basically nothing!! Always aim for a low double figure. the old accepted standard was 10 ohms, but that was with decent sized and lengths of earth rods. Just as important as low Ra values is the stability of the earth rod position(s) The deeper the better, for both stability and Ra values...
Reply to External earth fault loop tt system in the UK Electrical Forum area at ElectriciansForums.net