Evening all could anyone please tell me the the maximum ze for tt systems the jobs entail Rec cut out fuse bs88 16a to feed 1x 30 ma rcd fuse spur for feeding socket outlet what should the max ze be please
 
really 1667 ohms the some are coming up like 180 odd ohms was worried but our manager said it was fine with the 30ma protection and 1667 is what he said we work to I always thought a ze on tt had to be less than 21 ohm
 
I went to a job the other day to change a broken plug socket and a zs revealed a reading of 480ohms, it was on a tt but they didn't want me to do anymore as they were having an extension done in a couple of months time so it could get sorted then! I didn't feel overly comfortable leaving it but it was all protected by a single 30mA rcd and i advised them of the danger if the rcd were to fail but they didn't seem that concerned, what can you do
 
The lower the better but I seem to recall on a regs course that the preferred maximum is no more than 200ohms.
once job is complete do a rcd test with an approved meter if it trips out in the required parameters then ok.
 
6 Hours later!! lol!!


The lower the better but I seem to recall on a regs course that the preferred maximum is no more than 200ohms.
once job is complete do a rcd test with an approved meter if it trips out in the required parameters then ok.

Another Reg bible basher!! with no understanding of a TT system!!

I am still confused my zs can be upto 1667 ohm at the socket but what about my Ra from electrode to incoming supply to spur from rec fuse would tis be 21ohm or 100ohm or 200ohm?​




21 ohms is the max for sub-station earthing and the like, but you'll never see a value anywhere near that high at a sub-station.

The 100 and 200 ohm values that are thrown about by the NICEIC and BS7671 are one almighty joke, and good for basically nothing!! Always aim for a low double figure. the old accepted standard was 10 ohms, but that was with decent sized and lengths of earth rods. Just as important as low Ra values is the stability of the earth rod position(s) The deeper the better, for both stability and Ra values...
 
6 Hours later!! lol!!




Another Reg bible basher!! with no understanding of a TT system!!




21 ohms is the max for sub-station earthing and the like, but you'll never see a value anywhere near that high at a sub-station.

The 100 and 200 ohm values that are thrown about by the NICEIC and BS7671 are one almighty joke, and good for basically nothing!! Always aim for a low double figure. the old accepted standard was 10 ohms, but that was with decent sized and lengths of earth rods. Just as important as low Ra values is the stability of the earth rod position(s) The deeper the better, for both stability and Ra values...

Better late than never bonny lad!! :)
 

Reply to External earth fault loop tt system in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
321
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
848
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
971

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top