Fault on external lighting roughly 12 lights around a building, RCBO tripping, my tester only goes to 200 Megger Ohms
L-N is 0 Megger
N-E is greater than 200 Megger
L-E is greater than 200 Megger
LN-E is 150 Megger

Now tested insulation from board and roughly found the middle light with 1 cable so must be joint boxes somewhere I can’t find, went to a light further and found a joint box and tested each leg and was getting near to no Megger Ohms on each side, any further ideas?
 
I ap
i first do a continuity test L-N to see if there are any loads connected. sometimes there may be a neon switch will read something like 23K ohms. ( or is it 2.3 K, i forget, bloody dementia)
all loads are still connected they all have emergency back up too, so L-N I’m getting 0, have done LN-E and getting over range, all I can do is take the rest of fitting apart and bypass all circuitry or go to one in middle and re test there but will possibly give me same readings
 

Reply to External lighting fault in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
953
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
It is actually specified in BS7671 that the cpcs must be connected to all other sources of earth.
Replies
9
Views
773
  • Question
When you did the further testing and got the 0.06 reading were the CPC's back in the consumer unit? Really when testing you should leave the...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top