Fault on external lighting roughly 12 lights around a building, RCBO tripping, my tester only goes to 200 Megger Ohms
L-N is 0 Megger
N-E is greater than 200 Megger
L-E is greater than 200 Megger
LN-E is 150 Megger

Now tested insulation from board and roughly found the middle light with 1 cable so must be joint boxes somewhere I can’t find, went to a light further and found a joint box and tested each leg and was getting near to no Megger Ohms on each side, any further ideas?
 
Fault on external lighting roughly 12 lights around a building, RCBO tripping, my tester only goes to 200 Megger Ohms
L-N is 0 Megger
N-E is greater than 200 Megger
L-E is greater than 200 Megger
LN-E is 150 Megger

Now tested insulation from board and roughly found the middle light with 1 cable so must be joint boxes somewhere I can’t find, went to a light further and found a joint box and tested each leg and was getting near to no Megger Ohms on each side, any further ideas?
Are all the lamps/bulbs disconnected when you are testing? 0 mega ohms could be a dead short or it could be some value less than 1 mega ohm.
 
Are all the lamps/bulbs disconnected when you are testing? 0 mega ohms could be a dead short or it could be some value less than 1 mega ohm.
There all still connected, there’s something like 12 lights and was getting 0 Megger at the board L-N and when tested at light in the middle of circuit something like 0.06 Megger
 
If the luminaires are still connected you cannot obtain a line/neutral reading, forget that. If you are 100% certain the neutral is isolated at the dist board and you are getting zero meg to earth then you need to break down the circuit to find the fault.
 
If the luminaires are still connected you cannot obtain a line/neutral reading, forget that. If you are 100% certain the neutral is isolated at the dist board and you are getting zero meg to earth then you need to break down the circuit to find the fault.
Thanks, and was only 0 Megger L-N, all others were off the scale so all good must of been cause I left al lamps in, need to open all fittings and go from there, thanks again
 
Only been testing on 250v sorry mr know it all

You were carrying out the test incorrectly regardless of what voltage you tested at,my point still stands. Testing at 250V instead of 500V just further proves that you don't understand the test you are carrying out.

I don't know it all or expect anyone else to know it all, but I do expect an electrician to know the basics of the science of electricity and understand insulation resistance testing.
 
i first do a continuity test L-N to see if there are any loads connected. sometimes there may be a neon switch will read something like 23K ohms. ( or is it 2.3 K, i forget, bloody dementia)
 
Only been testing on 250v sorry mr know it all
Only been testing on 250v sorry mr know it all
Being a bit harsh in your reply there Bradley, I sent you a PM which you haven't responded to, trying to help you with your terminology, a thanks would be nice, but not holding my breath, for a reply anytime soon.
 

Reply to External lighting fault in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
951
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
It is actually specified in BS7671 that the cpcs must be connected to all other sources of earth.
Replies
9
Views
773
  • Question
When you did the further testing and got the 0.06 reading were the CPC's back in the consumer unit? Really when testing you should leave the...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top