Called out this morn, burning smell from shower pullswitch.

Got there, inspected, arcing on line conductor load side in switch. Loose connection or moisture. re-terminated and connected. Tested from shower, conductors disconnected. Results satisfactory. Did Minor Works Cert for them.

Shower circuit: split from mains in Henley blocks to sep rcd enclosure - 30mA, then 40A mcb.

Confusing part coming up. Why was there an extra 4mm cpc run through the switch and shower? I initially thought perhaps poorZs. Test showed the extra cpc only made 0.02ohms difference to Zs. Also, this extra cpc didn't run back to the main earth in the shower rcd unit. I presume it went back to the main c/u (in a bit of a hurry, didn't have time to check inside main c/u).

Is it do do with the time/current characteristics of the 40A Type B being 200A for 5sec, and the 4mm cpc in the 6242Y not being able to handle this?

I've done a few showers, seen a few more, but not come across this before. Perhaps 16thEd Regs?

Thanks chaps, any advice gratefully accepted.
 
Called out this morn, burning smell from shower pullswitch.

Got there, inspected, arcing on line conductor load side in switch. Loose connection or moisture. re-terminated and connected. Tested from shower, conductors disconnected. Results satisfactory. Did Minor Works Cert for them.

Shower circuit: split from mains in Henley blocks to sep rcd enclosure - 30mA, then 40A mcb.

Confusing part coming up. Why was there an extra 4mm cpc run through the switch and shower? I initially thought perhaps poorZs. Test showed the extra cpc only made 0.02ohms difference to Zs. Also, this extra cpc didn't run back to the main earth in the shower rcd unit. I presume it went back to the main c/u (in a bit of a hurry, didn't have time to check inside main c/u).

Is it do do with the time/current characteristics of the 40A Type B being 200A for 5sec, and the 4mm cpc in the 6242Y not being able to handle this?

I've done a few showers, seen a few more, but not come across this before. Perhaps 16thEd Regs?

Thanks chaps, any advice gratefully accepted.

It may have been someone attempt at supplementary bonding, I been asked to bond between light and shower outlet if you could touch light from shower, also been asked to bond from shower to shower basin metal waste used to be NICEIC requirement.
 
Although i respect you own judgement and may be teaching you to suck eggs but if you had a loose cable check there is no heat damage to the switch and cable if their is then it would be wise to replace pullswitch and strip back beyond damaged cable when reterminating as the heat changes the properties of the metal and sometimes you loose the contact force within the switch thus expect it to happen again even though terminals tight.
 

Reply to Extra CPC on Shower Circuit in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
298
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
848

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top