Hi
Been asked by a customer to wire up a 15kw extraction motor the only figures i have at present are 3 phase 400v
Start current star delta 80.7 Amps
Run Current 26.9 Amps
done a quick cable calculation

15000/1.732*400*0.8=27.06A per phase

Will be using 3core Swa cable and the run is about 80 metres looking in the brb refer table4d4a comes at using 4mm seem a tad small to me considering the run length?
I haven't done alot of Industrial calculating so am getting stuck any help would be appreciated Thanks
 
Personally on a distribution cable like that I would go up to 10mm for that long a run.

Though you will have a large inrush current of 80 amps as long as you can conform to Regulation 525.4 regarding product standards or manufacturers recommendation then you should be ok.

As you are just using 3 core I assume you are going to be utilising the SWA as the CPC. You will find that a normal 70c SWA may not give you a good enough CPC, you will have to do the Adiabatic equation, or run a seperate CPC. XPLE should be fine though. The XPLE will give you an higher current rating capacity, but the VD per meter is virtually the same.

Is the controls for this motor remote? ie 80 metres from the motor, check to see if you need a neutral at the motor end. perhaps for a brake or something.
 
Thanks Malcolm
I was thinking more along the lines of a 10mm 3 swa due to the length of run,and the high start up current.

I'm a bit rusty on calculating cable sizes and protective devises, Would any of you like to help me out?
I've been studying a pvc_xlpe.pdf.
Looking to see if the armour would be a suitable earth.
 
According to my table data on SWA cable, a 3 core 10mm PVC/SWA/PVC cable has a SWA CSA of 44, the minimum required CSA for the armouring to meet CPC requirement being 22.6. So i would say that the armouring can indeed be utilised as your CPC....
 
Thanks Engineer54
John
Both the 6mm and 10mm are within the 5% for volt drop of 20 volts?

Calculation for the protective devise rating.
Iz>In
brb states 58A cable rating
 

Reply to Extraction motor in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

I got this all wired in and working thanks to the help from James, absolutely top man. Do have a small issue with current imbalance atm, L3...
Replies
10
Views
2K
  • Question
Ok Dave thanks, no more accidents yet 🙏😂….
    • Like
    • Informative
    • Winner
Replies
6
Views
2K
This is important. If the overload was originally connected in the supply lines it needed to be set to the 38A FLC, not the 0.58x FLC (22A) which...
Replies
19
Views
6K
With the motors connected 'star', and run from the 208V supply, they'd only be 10% down on voltage. I've come across worse on farms.
Replies
4
Views
1K
  • Question
asking advice: I had the AM2 assessment today and there’s a couple of things I wanted to check with someone that may have done this recently. the...
Replies
0
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks