P
pjb1
Hi
Been asked by a customer to wire up a 15kw extraction motor the only figures i have at present are 3 phase 400v
Start current star delta 80.7 Amps
Run Current 26.9 Amps
done a quick cable calculation
15000/1.732*400*0.8=27.06A per phase
Will be using 3core Swa cable and the run is about 80 metres looking in the brb refer table4d4a comes at using 4mm seem a tad small to me considering the run length?
I haven't done alot of Industrial calculating so am getting stuck any help would be appreciated Thanks