A customer rearranged some kitchen units, exposing a copper section of the main waterpipe. It's just over a foot long(rest of house is Qualpex). However it's unbondedI carried out an Fli test and it maxed out. I next carried out an IR test and got a, reading of 7000 ohms. A little high for a waterpipe I thought. Double checked with a second test and got same reading. OK, a little bit of copper pipe running in some very dry concrete.
However the reading is still way to high to leave it unbonded and the CU is right at the other end of the house.

What other options might I have?
Get a plumber to replace the copper with Qualpex?
Bond the copper pipe to a local socket?
All suggestion welcome
 
Cover it in insulating tape?
I don't understand it when you use simple language Lucien.

Do you mean 'Introduce a jacket of insulating swathe'?
 
I don't understand it when you use simple language Lucien.

Do you mean 'Introduce a jacket of insulating swathe'? .
but not any old insulating swathe. got to be M&S swathe. (what is swathe? ).
 
I shouldn't admit this but my brain wandered to trying to think of an inexpensive plumbing accessory that requires an earthed electrical connection that could be installed inline on the pipe and legitimately powered by a spur....thus bringing the potential to earth down so when you test it its suddenly fine...!
I couldn't come up with one, a two port zone valve locked open was the closest I got!
 
I shouldn't admit this but my brain wandered to trying to think of an inexpensive plumbing accessory that requires an earthed electrical connection that could be installed inline on the pipe and legitimately powered by a spur....thus bringing the potential to earth down so when you test it its suddenly fine...!
I couldn't come up with one, a two port zone valve locked open was the closest I got!
self tapper through pipe, ring crimp to stop the leak. (well, wet-pants screw up our gear. REVENGE TIME).
 
I just hope that stop cock won't need 'taping up', too. 😉
Stop cocks are like RCDs. They sit there for years and then you want the untested thing that has had no exercise to actually do something useful and nope....either stuck solid or leaks when you move it.
 

Reply to Extraneous part issue? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
949
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
989
  • Question
I've discussed this with the OP directly as we are friends, but for anyone searching in the future, the service manual suggests that this...
Replies
2
Views
886

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top