A customer rearranged some kitchen units, exposing a copper section of the main waterpipe. It's just over a foot long(rest of house is Qualpex). However it's unbondedI carried out an Fli test and it maxed out. I next carried out an IR test and got a, reading of 7000 ohms. A little high for a waterpipe I thought. Double checked with a second test and got same reading. OK, a little bit of copper pipe running in some very dry concrete.
However the reading is still way to high to leave it unbonded and the CU is right at the other end of the house.
What other options might I have?
Get a plumber to replace the copper with Qualpex?
Bond the copper pipe to a local socket?
All suggestion welcome