Supposing I have my Main Incomer (4c70mm2) at one side of a very large warehouse.

My incoming water is on the far side.

My Main Earthing bond (35mm2) is from the incomer to the M.E.T.

I am going to equipotential bond my Structural steel close to the M.E.T. (25mm2)

Can I then come off the Structural steel on the far side to bond to the water incomer?

Or would I need to run a seperate 25mil all the way from the M.E.T.?

How many other services could I use the Structural steel to bond in the same way? Is this acceptable?

Thanks in advance!
 
Surprised no-ones clocked this one...
All incoming services should have their own dedicated bond run to the MET.
Reasoning behind it is that say for whatever reason you lost your MET connection to the structure, in your situation by proxy you would also lose protection on the service, in this case the water pipe.
Hope this helps
 

Reply to Extraneous parts in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
227
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
687
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
638

Similar threads

I see no issue with this, it sounds like a relatively normal installation. The use of insulated and sheathed cables inside steel trunking is a...
Replies
5
Views
264
davesparks
D
  • Question
Why would the RCD fail … yes it can happen but then it may not. Without it you have no protection on the TT System
Replies
36
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top