Supposing I have my Main Incomer (4c70mm2) at one side of a very large warehouse.

My incoming water is on the far side.

My Main Earthing bond (35mm2) is from the incomer to the M.E.T.

I am going to equipotential bond my Structural steel close to the M.E.T. (25mm2)

Can I then come off the Structural steel on the far side to bond to the water incomer?

Or would I need to run a seperate 25mil all the way from the M.E.T.?

How many other services could I use the Structural steel to bond in the same way? Is this acceptable?

Thanks in advance!
 
Surprised no-ones clocked this one...
All incoming services should have their own dedicated bond run to the MET.
Reasoning behind it is that say for whatever reason you lost your MET connection to the structure, in your situation by proxy you would also lose protection on the service, in this case the water pipe.
Hope this helps
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

tigerpaul

Arms
-
Joined
Location
Tadley

Thread Information

Title
Extraneous parts
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
1

Advert

Thread statistics

Created
tigerpaul,
Last reply from
randyrat,
Replies
1
Views
1,808

Advert

Back
Top