Good evening,

This pertains to a four-bedroom property that is vacant due to minor redecorating. As part of this we employed a sizeable electrical company who completely went to town with the report and came back with 18 C2s for a non-period property that was redone in 2012. Furthermore the quote to remedy the 18 C2s exceeds £7,000. If that's the price, the property will not be able to recoup that cost even with many months of rent and we may as well give up and sell it.

Once an EICR report has been completed, is it allowed to ask another electrician to do another EICR report? If this second opinion flags up, say, 6 C2s, would I be done for the other 12 that the first electrician "spotted"?

Amidst the quote are:
  • £900 to replace two fire alarms. Apparently battery alarms are not sufficient; they must be wired in.
  • £1600 to replace 20 "class 1 construction" downlight fittings, as the extraneous parts aren't earthed. Apparently plastic replacements won't pass.
  • Up to £1000 to investigate loss of continuity in ground floor ring circuit. Apparently it may take a whole day to find where the continuity is lost.

We're at a loss and any comments by anyone who knows anything would be incredibly helpful!

Thank you so much.
 
Can you redact the the names and addresses on the EICR and post it here for review

I assume you have only listed the big cost items from the quote what does the remaining £3.5k buy you

How big is this property and how many sockets are fitted on the ground floor ring with £1000 to investigate the fault have they indicated what the repair might cost once they find the fault
 
Although I don’t know London prices, but to me that is extortionate.
Get a second quote from another electrician, but if it was all done in 2012, there can’t be much wrong.

As for the faults listed....

you can get lithium battery powered smoke alarms for £80~ with a radio interlink (when one goes off they all go off) diy installation. If you don’t want mains powered. (Check this before renting out that it would be acceptable)

£80 per downlight seems steep. Sometimes the type of downlight is ok, but the wiring itself is wrong. (Eg, the installer didn’t connect the earth wire through to every light position.

A couple of hours to trace the fault. It’s just taking sockets off and finding the break, but the fix could take a lot more.
 
Even London rates of £600 a day , I can’t get to £7000 for the work you have been quoted

I could do 2 x mains smokes hard wired dedicated circuit £550
Replace 20 x DL £1200
Rewire up to 20 x sockets on the ground floor £2000

so my bill would only be £4000 absolute max
 
Thank you all so much for all these thoughts. I have reviewed the information more and it's actually £6000 for remedial works, as the £7000 includes £1000 for the EICR report itself. The day labour rate is £800 + VAT.

The ground floor is about 450 sq ft. I'm not entirely sure how many sockets there are. The property is small for having four bedrooms.

I have uploaded the screenshots for the items here. Please let me know if it's unreadable - it looks clear in the text editor but I don't know how it will come out. Thank you!

[ElectriciansForums.net] Extremely detailed EICR resulting in £7000 remedial works quote

[ElectriciansForums.net] Extremely detailed EICR resulting in £7000 remedial works quote
 
The listing of 'old' and 'discoloured' items tells me everything I need to know about the agenda of the people doing that report. Assuming the test results are OK, the lack of RCD protection could most likely be remedied in a day by changing the consumer unit.

The fact that the lack of RCD protection features multiple times, I think supports my view.

Get a recommendation for a spark you trust from someone and have them take a look at the report and give you a quote to fix what actually needs fixing.
 
Some list there.... pity they hadn’t proof read it beforehand. (Item 15, “up” rating??? That’ll be IP)

If the whole place was redone in 2012, there should be nothing wrong with the switches and sockets unless they’re physically damaged, which he has picked up in a couple times. “Discoloured” isn’t really under the BS7671 remit.
 

Reply to Extremely detailed EICR resulting in £7000 remedial works quote in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
311
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
936

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top