If a ring final is RCD protected, and a spur is taken outside the EZ need that spur be seperatly RCD protected, IE at point of use by a RCD socket or other method
Pict
 
i would say no. e.g. if you are fitting an outside socket to an RCD protected circuit, by fitting a 2nd RCD you would have no discrimination.
 
I was thinking the same,But if the ring is prtected by a 80A/30mA and I use a 25A/30mA I know that discrimination is met at the current rating but does discrimination at the trip current have to be met.I cant see how unless I used a 100mA RCD at the board but that raises more issues
Pict
 
you're correct. however , having no RCD discrimination is not a safety issue, more a matter of inconvenience. the only good way would be to feed the outside RCD socket from a non-RCD way in the board, but then you'd have to run the cable surface.
 
Problem is this is to a cold room outside and the cable is buried in plaster on the inside then the spur goes through a hole in the wall in 2.5 T&E
I feel that as it is part surface part buried any future issue will take out the whole kitchen and I would like to limit this by a RCD I suppose it's a judgement call at the end of the day, but your right if safety in not compromised it should be fine
Pict
 
Problem is this is to a cold room outside and the cable is buried in plaster on the inside then the spur goes through a hole in the wall in 2.5 T&E
I feel that as it is part surface part buried any future issue will take out the whole kitchen and I would like to limit this by a RCD I suppose it's a judgement call at the end of the day, but your right if safety in not compromised it should be fine
Pict

Again ...No!! The likelihood is that any fault will take out Both 30mA RCD devices, not one or the other!!! So it will take out the whole kitchen!!
 
Last edited by a moderator:
if the cable is already installed from the RCD protected RFC then you're shafted. as eng54 says, a fault in the cold room will take out the kitchen. having said that, at least they will know that it's tripped.
 
you could take the RFC off RCD or replace the RCD with a 100mA time delay one, but that would be leaving the installation less safe than it was before.
 
Well at present, it would appear the spur is allready RCD protected.
Removing the RCD protection from the RFC would mean that the installation still complied with BS7671, however as Tel says, it would be less safe.
It looks like your options are to the leave the RCD protection as is, which would trip the RCD for the RFC if there is a fault on the spur.
Or run a new Radial circuit either with or without RCD protection.
 
I was thinking the same,But if the ring is prtected by a 80A/30mA and I use a 25A/30mA I know that discrimination is met at the current rating but does discrimination at the trip current have to be met.I cant see how unless I used a 100mA RCD at the board but that raises more issues
Pict

you have no discrimination at all the 80a & 25a are just the max load they can switch not an overload rating such as an mcb.

you have no way of getting any discrimination with the setup as it is. You also can't get discrimination by changing the current rcd to 100mA, you would need to fit a s type rcd (time delayed) up front.

Personaly I would say they are better off having it on the 30mA rcd ring as you don't want the cold store tripping out and no one knowing about it until its all go warm. If they don't like that they will have to have a new circuit from the DB.
 

Reply to EZ and spur in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
124
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
910
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

Are you sure the existing outside socket is on the ring, and not already a spur? I tend to place a switch fuse on the ring inside so that the...
Replies
1
Views
201
Yeh fuseboxshop.delivery up here only takes 3 days
2
Replies
25
Views
986

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top