fabric covered cables | on ElectriciansForums
Discuss fabric covered cables in the Australia area at ElectriciansForums.net
A
andekoch
Just done a PIR and found the lights wired in old fabric covered cables. They passed the IR test but I have still marked them as a code 2 and told the home owner to replace them since the fabric disintegrates when moved and no double the insulation does the same. Was very tempted to mark it down as a code 1.
Also found metal switches (very old copper and brass) plus no cpc and put that down as a code 2 as well. Very tempted to have made that a code 1 though but already done the cert.
what would you mark them down as?
The possibility of a plate screw (or light fitting) becoming live ,then a person coming into contact with it, then conducting it through themselves to earth and getting a shock or being killed, is I believe, pretty long odds.
Thats the reason I would rarely think to give a light circuit without a cpc a code 1
The failing of the insulation may be another matter
If you haven't already seen it.there is guidance for us at the safety council for this,also how to test that light circuit for best possible safe use,with additional comment to recomend rewiring
Here is a link,if you want to compare your coding with them
Everybody codes things as they see danger themselves,but personally i would not code 1 your example
http://www.esc.org.uk/pdfs/business-and-community/electrical-industry/BPG4_08.pdf
Scroll to page 12
Its not the fact that its got no CPC to worry about as ezzee has said they are VIR ,and they deteriorate rapidly these cables could be pre 1930's so im sorry to say the house is in need of urgent rewire , you must advise the house holder , and cover your back side , i would class this as a Code 1 ,if the cables are singles wired throught out in the loft it has a very hi possability for a fire , in fact not seeing the installation im asuming the cables are in the lofts , consideration should be given to serving a danger notification, i have seen these cables in Lofts no isulation as its all dropped off just fibre and bear wire scary, cover your self mate
I did tell the home owner that this circuit (is only on the lounge and hall lights) was in need of a rewire. I refused to change ot touch anything connected to the cables in case they fall appart (the switch face plates could be removed without disturbing the cables).
the bit a saw in the cu seems to be 'reasonable' ie not crumbling insulation but the fabric outer is very brittle so one of the insulation layers is definately dead. could also be passing the insul resistance tests if not touching due to the excellent insulation propeties of air, hmm. just a pity air does not prevent contact.
the property is a ground floor flat in a converted house so cables will run in the floor void between the flats.
Reply to fabric covered cables in the Australia area at ElectriciansForums.net
Hello oscar21, When I wrote about cables heating up I meant that IF a cable heated up that heat could not dissipate correctly if the cable was...
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...