Hi all, I recently failed my installation of swa cable and TP&N socket outlet and not sure why. Passed the rest. Any advice, It says:

-did not complete connections/terminations to industry standards

-identification/labelling to the required standard.
 
i presume that the swa used was 4 core?


L1 brown
L2 black
L3 grey
N blue

if you have got the colours in the wrong terminals, it would be a fail.

earth (cpc) needs to be well terminated to the gland via a banjo and a nut/bolt or by another standard connection such as an earthing (piranha) nut.

right size crimp on the cpc link
identified link as PE with tape or sleeve

no exposed copper showing from the terminals.

as above, was the right gland used and correctly installed?

the only person that can tell you where you went wrong is the examiner, have you asked them?
 
Upvote 0

Reply to Failed am2 on swa circuit? in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
315
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
295
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
361

Similar threads

  • Question
When I did my AM2, I had it drummed into me that I had to follow Guidance Note 3 carefully. So, did you follow the guidance in GN3 for checking...
Replies
1
Views
1K
I assume said contractor is part of a Part P scheme (NICEIC, Napit, few others..) in which case complain to them. They'll investigate (in theory)...
Replies
10
Views
831

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top