As the title suggests, I got my am2 results last week and passed everything apart from earth loop impedance but I've no idea why. Im sure I disconnected the main earth and tested all the phases etc so I'n just wondering if theres any additional things they require me to do in the Am2 that I didnt know about? Because if I was to resit the test now I would do everything exactly the same!

I've tried asking the am2 centre but they just said they cant provide any more feedback. But my JTL assesor has suggested it maybe because I didnt have the regs book open on the page with the required earth loop readings? But I'm not sure as I've asked other people who have passed and they said they didnt do that either.
 
Why did you disconnect the main earth? unless you were doing a ZE? that would make sence
 
Assuming you were measuring the external earth fault loop impedance of the installation.
Were you measuring at the incoming supply?
Did you ensure that the main supply isolator was off so that the installation was not energised during the test?
Did you record the highest reading obtained from all the tests?
Did you identify if the reading recorded was a satisfactory reading?

that is all I can think of to start with.
 
Just to point you in the correct direction:-

Q. What earthing arrangement is it and does it have an effect on your testing?

Q. Dose the number 0.8 spring to mind for your exam?

Have a look at appendix 14 and the regs it directs you to. Happy reading :wink:
 

Reply to Failed Earth Loop on AM2, not sure why? in the Electrical Course Trainees Only area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
669
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

I think I’ll just buy a DOL and play around with it. I don’t remember ever working with one in the real world, I must be missing something obvious...
Replies
10
Views
200
  • Question
When I did my AM2, I had it drummed into me that I had to follow Guidance Note 3 carefully. So, did you follow the guidance in GN3 for checking...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top