OP
sharpy1983
Hi Des, that's why I've asked the question on this thread,
I suppose that seeing the cpc cut and the failure of IR between both live conductors and earth caused me concern but I can see that it is a degraded cable which will be put in for a replacement.
the general consensus is that, if the Zs complies, then the circuit should remain live but should be noted in the observations that the cable requires replacing due to the IR failure.
What code would you enter in the obs part of the report? C1,c2,or c3?
I suppose that seeing the cpc cut and the failure of IR between both live conductors and earth caused me concern but I can see that it is a degraded cable which will be put in for a replacement.
the general consensus is that, if the Zs complies, then the circuit should remain live but should be noted in the observations that the cable requires replacing due to the IR failure.
What code would you enter in the obs part of the report? C1,c2,or c3?