Hi just wondered if the cables supplied by a TV manufacturer for the many TVs in our office block which have a half PVC shroud on the plug pins should have failed because of no earth? They were supplied with the TVs so we assumed they would pass ok. All the TVs are brand new, the PAT tester said they had no earths! Are these the correct leads?
 
If the TVs are class II (double insulated) then they don't need an earth. Look on the TV for a symbol that looks like a square inside another square. If you find it this means the TV is class II
 
Thanks, that means the guy failed all the leads and probably didn't check the TVs for double insulation, and made us change all the leads to ones with earths
 
Hi jaguar - seem to have got a bit tangled up in this thread somehow. Its a pity people keep referring to "kettle" leads and not IEC leads if that's what they mean. Most kettles these days are wired into their bases.

A picture of actual lead termination that started the thread would be most useful - then it could be determined if in fact there was an earth terminal and of course a corresponding socket in the tv.

I do come across 2 pin "IEC type" cords which are used with medical nebulisers - and these (nebulisers) as well as indicated as being double insulated have 2 pin "IEC type" sockets. And of course the 2 pin "IEC type" cords will not fit into an IEC socket (3 pin).
 

Reply to Failing a kettle type lead used on TVs in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
354
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
905
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top