Using the diagram it is straight forward enough to see the water level sensor cable in the top left of the printed circuit board, which then runs into the top of the sensor, which can be seen in the last picture.

How does the flood switch work though and why can't I see any evidence of it on the PCB?, marked cables 7 and 8 on the drawing.

The switch opens in "alarm", but physically what is going on here? Where are the cables shown in the drawing?
 
Looking at the PCB there's no cables connected for the alarm. Circled in red.

[ElectriciansForums.net] Fan Coil Unit Schematic Diagram Interpretation (Pics)

Is there an alarm circuit?
 
Those are the supply terminals (Line and Neutral) for the PCB though, which were disconnected in order for the PCB to removed from it's housing to be photographed.

The L and N are looped out of the incoming L and N terminals, which come from a switched spur, which feeds the motor as well.

it seems to me as though the alarm circuit doesn't even exist, the drawing shows the alarm from the PCB, but looking at the physical PCB there is no evidence of it.
 
This might be the pins here, this probablbly say condensate alarm or someting, I can only se 'sate.

Check to see if the above pins go to the relay contacts via the PCB tracks.
 

Attachments

  • [ElectriciansForums.net] Fan Coil Unit Schematic Diagram Interpretation (Pics)
    SATE.jpg
    181.6 KB · Views: 38
Last edited:
My bad, tired eyes, too much looking at three phase motor diagrams. I think I need a pint as just had another look and I can now see the layout.
 
Probably an option when the unit was built and this unit didn't have it.

I've sen many of these F.C.U's mainly IMI and never seen the alarm cicuit used even if it when the pcb had the connections for it.

The best way to warn of it's immenent failure is to let the condensate overflow thro' the ceiling.
People react to water better than to an alarm.
 
Okay, thanks for the replies and yes that very well might be the alarm cables, highlighted in the reply above. In fact, it definitely is, my memory has just been jogged, and those cables went straight to empty terminals on the same strip that the motor speed cables are connected together.

How does the alarm work then hypothetically, because from the diagram is doesn't make a whole lot of sense. The contacts open, but what are those contacts opening exactly? It just doesn't seem clear.
 
I would guess it's just a potential free contact that can be used to trigger a remote alarm. There would need to be another PCB or alarm module as the contact is normally closed and opens on alarm. This is a failsafe configuration so if the alarm circuit becomes open circuit due to damage it will trigger.
 
It's failsafe and being open on alarm stops anyone connecting a lamp directly to the contact and overloading it, you'd have to use a relay with a almp.
If it was used as a signal to a BMS system it wouldn't matter whether it's open or closed on alarm it could be set as an alarm input either way.
 
One more question, looking at the schematic for the motor, why does it only show the incoming Neutral, but no live like it does for the L and N incoming on the PCB schematic?
 
One more question, looking at the schematic for the motor, why does it only show the incoming Neutral, but no live like it does for the L and N incoming on the PCB schematic?

It does, sort of, marked High, Med, Low, these will be Switched lives, or they could be PWM lives.
 
That makes perfect sense, but I could have sworn there was separate L,N+E coming from the switched spur, which feeds the whole setup, including the motor, the speed wires not included.

I need to go back and take another look.
 
It's failsafe and being open on alarm stops anyone connecting a lamp directly to the contact and overloading it, you'd have to use a relay with a almp.
If it was used as a signal to a BMS system it wouldn't matter whether it's open or closed on alarm it could be set as an alarm input either way.

What do you mean by connecting a lamp directly to the contact and overloading it? If the FCU is in a ceiling space what good would a lamp do as an alarm signal? Some sort of sounder makes more sense. It's all hypotehtical of course, because the alarm isn't even connected.

I vaguely get what you're saying about a BMS connection option, as then it could be monitored remotely via a laptop or such.
 

Reply to Fan Coil Unit Schematic Diagram Interpretation (Pics) in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
791
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
817

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top